To add to this point,  a customer inadvertently wired a 100 amp 240 vac 
Tesla charger circuit into an Outback backup system.  We later had to 
rebuild the inverters because they had cooked the 60 amp rated transfer 
relays.  The 50 amp breakers had tripped occasionally, but apparently 
not enough to save the relays.  The relays were not completely gone, but 
were no longer reliable.

Ray Walters
Remote Solar
303 505-8760

On 8/8/19 2:14 PM, Lones Tuss wrote:
>
> I happen to like the 50 amp breaker as it should trip before the 
> relays get stressed.
>
> I hope this helps.
>