[RE-wrenches] Pass-through state Dual FXR system

Jerry Shafer jerrysgarage01 at gmail.com
Sat Aug 3 19:52:04 EDT 2019


Mac
Is this site on Optics, what is the state of charge when the genny turns
on. Did you use the outback white paper to set up the system with the BPE
Batteries, this might be helpful.
Jerry
Jerry

On Sat, Aug 3, 2019, 2:35 PM Mac Lewis <maclewis1 at gmail.com> wrote:

> Hi Wrenches,
>
> I've got an issue that I'm remotely trying to troubleshoot but I must be
> missing something.
> Specs:
> Off-grid
> Dual Outback FXR 3648s recently installed
> FM100, with about 4k of solar
> 2 x 16 kWh Blue Ion Batteries, installed this past week
> Kohler 14 generator
> Outback Mate 3s
>
> The issue is that the FXR inverters aren't charging the batteries when the
> generator is running, they are just passing the power through to the
> loads.  I have verified that AC Input is in "Use" not "Drop" when generator
> is running, I have disabled all of the advanced charging (ie Global charge,
> float coordination, auto-charge termination and auto grid-tie control) .  I
> have told it to "start bulk" both remotely and through the owner on site.
> I have done a reboot multiple times of the whole system as well as the Mate
> 3s.  I even had the owner try a factory reset and firmware update on the
> Mate 3s.  The firmware was successfully updated and it appears the factory
> reset on the mate.
>
> Nothing has changed how it behaves with the generator, generator just
> follows the load and no AC charging takes place.  Oddly, this was working
> fine when we left, we had topped the batteries off with the generator.
>
> Any ideas what I might be missing?
>
> Thanks for your suggestions
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190803/567177cb/attachment.htm>


More information about the RE-Wrenches mailing list