[RE-wrenches] Pass-through state Dual FXR system

Mac Lewis maclewis1 at gmail.com
Sat Aug 3 18:53:12 EDT 2019


The Bulk setting is 55.2V, the battery voltage is around 53.  Generator
quality is good, tried with two different generators, same result.  These
batteries can soak up current without the voltage changing much, great
charge acceptance.  The BMS is reporting ~40% SOC.  The Outbacks just stay
in "pass through" mode as though they think the batteries don't need it.
They don't respond when I tell them to bulk charge.

On Sat, Aug 3, 2019 at 4:40 PM Glenn Burt <Glenn.burt at glbcc.com> wrote:

> It almost sounds like the inverters are not happy with the quality of the
> generator output.
>
> -Glenn
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
> ------ Original message------
> *From: *Mac Lewis
> *Date: *Sat, Aug 3, 2019 5:35 PM
> *To: *RE-wrenches;
> *Cc: *
> *Subject:*[RE-wrenches] Pass-through state Dual FXR system
>
> Hi Wrenches,
>
> I've got an issue that I'm remotely trying to troubleshoot but I must be
> missing something.
> Specs:
> Off-grid
> Dual Outback FXR 3648s recently installed
> FM100, with about 4k of solar
> 2 x 16 kWh Blue Ion Batteries, installed this past week
> Kohler 14 generator
> Outback Mate 3s
>
> The issue is that the FXR inverters aren't charging the batteries when the
> generator is running, they are just passing the power through to the
> loads.  I have verified that AC Input is in "Use" not "Drop" when generator
> is running, I have disabled all of the advanced charging (ie Global charge,
> float coordination, auto-charge termination and auto grid-tie control) .  I
> have told it to "start bulk" both remotely and through the owner on site.
> I have done a reboot multiple times of the whole system as well as the Mate
> 3s.  I even had the owner try a factory reset and firmware update on the
> Mate 3s.  The firmware was successfully updated and it appears the factory
> reset on the mate.
>
> Nothing has changed how it behaves with the generator, generator just
> follows the load and no AC charging takes place.  Oddly, this was working
> fine when we left, we had topped the batteries off with the generator.
>
> Any ideas what I might be missing?
>
> Thanks for your suggestions
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>


-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190803/ada91a96/attachment.htm>


More information about the RE-Wrenches mailing list