[RE-wrenches] Large Off-Grid Residential System and ciculating currents
Jason Szumlanski
jason at floridasolardesigngroup.com
Thu Jul 25 10:04:01 EDT 2019
Yeah, it's my understanding that the BMS systems on each parallel battery
deals with/prevents any imbalance.
As for 48V, I have been working with some that are 51V nominal and I know
there are some 60V solutions out there, so it's not so cut and dry to use
amp-hours. That's why I like talk in kWh to standardize.
I am taking the DoD into account when discussing my needs. I would probably
need a battery almost double the size in a lead acid chemistry!
On Tue, Jul 23, 2019 at 8:59 PM Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:
> William
> I have a few blue ion installs that was used for testing. I used eguage to
> monitor all DC in and out of each stack of 16k with no issues. The BMU
> manages everything and can be chained to each other to reduce or even
> prevent that issue. I have seen Blue Ions original stacks greater then 100k
> with years in the field, so with that cross bleed should be not a problem.
> Jerry
>
> On Tue, Jul 23, 2019, 4:59 PM William Miller <william at millersolar.com>
> wrote:
>
>> Friends:
>>
>>
>>
>> I am a complete newbie to any lithium technologies, so please forgive
>> some newbie questions:
>>
>>
>>
>> I am used to working in amp hours. If we are looking for a battery bank
>> in the range of 100 kWh, this converts to about 2,083 amp/hours at 48 VDC.
>> Is my arithmetic correct? An on-line calculator seems to confirm this.
>>
>>
>>
>> The biggest Blue Ion 2 battery is 16 kwh. At 48 VDC this is about 333
>> amp/hours. This is like an L16. To get 100 kwh you would need to parallel
>> 6 strings of the 16 kWh batteries. I would never do this with L-16s. Is
>> anyone worried about circulating currents in this type of installation? Is
>> there technology to prevent one string from cannibalizing another?
>>
>>
>>
>> Here is another, more academic question below:
>>
>>
>>
>> In case I am using a term I made up (which is often the case), I define
>> circulating currents as currents flowing between parallel strings without
>> any outside influence. For example, if you disconnected all charging and
>> loads from an array with two parallel strings, unless the strings were
>> absolutely identical in electrical characteristics, there would be some
>> current flowing between the two strings. In my opinion this is the
>> Achilles heel in parallel strings. Also my opinions: 2. The more strings
>> you have the more chance there will be debilitating circulating currents.
>> 3. The older the batteries, the more the electrical characteristics will
>> vary and the more likely you will get higher circulating currents.
>>
>>
>>
>> It is my theory that if you can measure the circulating currents, or the
>> difference between parallel battery strings at any point in the operation
>> of same, you can get a read on the health of the strings. The more the
>> operating or idle currents diverge, the more one string will discharge the
>> other string. I guess this is some part of a battery management system. I
>> am guessing for the Blue Ion 2 to work in 6 parallel strings, they need to
>> monitor and control this difference in currents.
>>
>>
>>
>> We just installed a flooded battery array (2 strings of 4 Deka M6100-33
>> batteries). My plan is to retrofit the installation with a 1000A/100mv
>> shunt in the negative leads of both strings. With a DVM I can spot check
>> the circulating currents to learn about the battery health. In fact I have
>> a remote monitoring system
>> <https://millersolar.com/MillerSolar/Portfolio/Commercial/Cal_Trans/Remote/Remote_Control.html>
>> with some spare ports that can log these values. Might be an interesting
>> experiment.
>>
>>
>>
>> I appreciate any input on the viability of the Blue Ion 2 or other small
>> battery systems in multi-string installations. My customers are asking for
>> new technology, but I instinctively avoid parallel battery strings.
>>
>>
>>
>> William Miller
>>
>>
>>
>>
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>> Quote of the month: “As they age, batteries transition from energy
>>
>> storage devices to energy consuming devices.“ W. Miller
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
>> Behalf Of *Lou Russo
>> *Sent:* Saturday, July 20, 2019 1:50 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Large Off-Grid Residential System
>>
>>
>>
>> Blue Ion 2.0 with Outback or SMA. Works every time.
>>
>> Blue Planet's tech support is great, the warranty is even better.
>>
>>
>>
>> Aloha,
>>
>>
>>
>> Lou Russo
>>
>> lou at spreesolarsystems.com
>>
>> 808 345 6762
>>
>> Spree Solar Systems LLC
>>
>> CT-34322
>>
>>
>>
>>
>>
>>
>>
>> On Sat, Jul 20, 2019 at 10:36 AM Jay <jay.peltz at gmail.com> wrote:
>>
>> Hi Marco,
>>
>>
>>
>> Is the max surge 7kw, which is what is listed on line?
>>
>>
>>
>> Jay
>>
>> Peltz Power
>>
>>
>> On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf <marco at pvthawaii.com>
>> wrote:
>>
>> Seven to eight Tesla Powerwalls will get you that assuming that the
>> service entrance is no bigger than 200A.
>>
>>
>>
>> marco
>>
>> On Friday, July 19, 2019, Jason Szumlanski <
>> jason at floridasolardesigngroup.com> wrote:
>>
>> What are current popular options for battery based systems in the 100kWh
>> range? Preferably Lithium.
>>
>>
>>
>> Also, what inverter pairing is suggested with total stacked capacity of
>> 36kW, 120/240V?
>>
>>
>>
>> This is slightly larger than some of the systems I have worked with
>> recently. I'm a bit out of the loop, particularly on the battery side of
>> things.
>>
>>
>>
>> Jason Szumlanski
>>
>> Florida Solar Design Group
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190725/eff09fcc/attachment.htm>
More information about the RE-Wrenches
mailing list