[RE-wrenches] Large Off-Grid Residential System and ciculating currents
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Wed Jul 24 12:37:05 EDT 2019
Hi William,
I think you are smart to taking your time going to Lithium
Ion. I will let others work the math as each application/client is really
different.
I have a few clients offgrid who are early adopters and there
have been a few failures I have observed. For grid based Apps I really do
not concern myself because the grid is there for back-up. I will just say
the LFP battery management system is a new set of ways to lose power
offgrid. I am backing up my clients and have always done that at my offgrid
home.
Here is a link to the testing I have been watching since I started
testing advanced battery technology in the field for Schneider in 2016.
A
61% failure rate is not good news to me. Blue Ion And Discover is not in
the testing and the Muarta battery they use is doing very well.
https://www.solarquotes.com.au/blog/6th-canberra-battery-test/ [1]
Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [2]
e-mail offgridsolar at sti.net
[3]
text 209 813 0060
On Tue, 23 Jul 2019 15:08:49 -0700, William Miller
wrote:
Friends:
I am a complete newbie to any lithium technologies,
so please forgive some newbie questions:
I am used to working in amp
hours. If we are looking for a battery bank in the range of 100 kWh, this
converts to about 2,083 amp/hours at 48 VDC. Is my arithmetic correct? An
on-line calculator seems to confirm this.
The biggest Blue Ion 2 battery
is 16 kwh. At 48 VDC this is about 333 amp/hours. This is like an L16. To
get 100 kwh you would need to parallel 6 strings of the 16 kWh batteries. I
would never do this with L-16s. Is anyone worried about circulating
currents in this type of installation? Is there technology to prevent one
string from cannibalizing another?
Here is another, more academic
question below:
In case I am using a term I made up (which is often the
case), I define circulating currents as currents flowing between parallel
strings without any outside influence. For example, if you disconnected all
charging and loads from an array with two parallel strings, unless the
strings were absolutely identical in electrical characteristics, there
would be some current flowing between the two strings. In my opinion this
is the Achilles heel in parallel strings. Also my opinions: 2. The more
strings you have the more chance there will be debilitating circulating
currents. 3. The older the batteries, the more the electrical
characteristics will vary and the more likely you will get higher
circulating currents.
It is my theory that if you can measure the
circulating currents, or the difference between parallel battery strings at
any point in the operation of same, you can get a read on the health of the
strings. The more the operating or idle currents diverge, the more one
string will discharge the other string. I guess this is some part of a
battery management system. I am guessing for the Blue Ion 2 to work in 6
parallel strings, they need to monitor and control this difference in
currents.
We just installed a flooded battery array (2 strings of 4 Deka
M6100-33 batteries). My plan is to retrofit the installation with a
1000A/100mv shunt in the negative leads of both strings. With a DVM I can
spot check the circulating currents to learn about the battery health. In
fact I have a remote monitoring system [4] with some spare ports that can
log these values. Might be an interesting experiment.
I appreciate any
input on the viability of the Blue Ion 2 or other small battery systems in
multi-string installations. My customers are asking for new technology, but
I instinctively avoid parallel battery strings.
William Miller
Miller
Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com [5]
CA Lic. 773985
Quote of the month: "As they
age, batteries transition from energy
storage devices to energy
consuming devices." W. Miller
FROM: RE-wrenches
[mailto:re-wrenches-bounces at lists.re-wrenches.org [6]] ON BEHALF OF Lou
Russo
SENT: Saturday, July 20, 2019 1:50 PM
TO: RE-wrenches
SUBJECT: Re:
[RE-wrenches] Large Off-Grid Residential System
Blue Ion 2.0 with Outback
or SMA. Works every time.
Blue Planet's tech support is great, the
warranty is even better.
Aloha,
Lou Russo
lou at spreesolarsystems.com [7]
808 345 6762
Spree Solar Systems
LLC
CT-34322
On Sat, Jul 20, 2019 at 10:36 AM Jay wrote:
Hi
Marco,
Is the max surge 7kw, which is what is listed on line?
Jay
Peltz Power
On Jul 19, 2019, at 3:10 PM, Marco Mangelsdorf wrote:
Seven to eight Tesla Powerwalls will get you that assuming that the
service entrance is no bigger than 200A.
marco
On Friday, July 19,
2019, Jason Szumlanski wrote:
What are current popular options for
battery based systems in the 100kWh range? Preferably Lithium.
Also,
what inverter pairing is suggested with total stacked capacity of 36kW,
120/240V?
This is slightly larger than some of the systems I have
worked with recently. I'm a bit out of the loop, particularly on the
battery side of things.
Jason Szumlanski
Florida Solar Design Group
_______________________________________________
List sponsored
by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
[11]
Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[12]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[13]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [14]
Check
out or update participant bios:
www.members.re-wrenches.org [15]
_______________________________________________
List sponsored by Redwood
Alliance
List Address: RE-wrenches at lists.re-wrenches.org [16]
Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[17]
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[18]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [19]
Check
out or update participant bios:
www.members.re-wrenches.org [20] --
Links:
------
[1]
https://www.solarquotes.com.au/blog/6th-canberra-battery-test/
[2]
http://members.sti.net/offgridsolar/
[3] mailto:offgridsolar at sti.net
[4]
https://millersolar.com/MillerSolar/Portfolio/Commercial/Cal_Trans/Remote/Remote_Control.html
[5]
http://www.millersolar.com/
[6]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[7]
mailto:lou at spreesolarsystems.com
[8] mailto:jay.peltz at gmail.com
[9]
mailto:marco at pvthawaii.com
[10]
mailto:jason at floridasolardesigngroup.com
[11]
mailto:RE-wrenches at lists.re-wrenches.org
[12]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[13]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[14]
http://www.re-wrenches.org/etiquette.htm
[15]
http://www.members.re-wrenches.org
[16]
mailto:RE-wrenches at lists.re-wrenches.org
[17]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[18]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[19]
http://www.re-wrenches.org/etiquette.htm
[20]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190724/8ea4dff9/attachment.htm>
More information about the RE-Wrenches
mailing list