[RE-wrenches] 25 kW backfeed limit circuit
Jerry Shafer
jerrysgarage01 at gmail.com
Wed Jun 26 11:56:07 EDT 2019
Mac
I have done this, same as you with no issues from the utility (PG&E). I did
tell them it was behind a security pass code and could only be changed with
that code which was secure.
Jerry
On Tue, Jun 25, 2019, 9:47 PM Mac Lewis <maclewis1 at gmail.com> wrote:
> Hello Wrenches,
>
> I'm working with a small utility on a large residence for grid-tie solar
> with a wind-turbine. They have a 25 kW backfeed limit. Its a 4 stack
> radian system with about 25 kW of solar and 10 kW of wind. The wind is AC
> coupled Bergey and the solar is DC coupled with FM100s. My idea was to use
> the Radians to limit the solar to 15 kW and let the wind do its thing.
> However, the utility doesn't like the idea that this limit could be changed
> without their knowledge.
>
> Has anyone designed and/or implemented a backfeed limiting circuit that
> could knock some charge controllers off-line in case that 25 kW limit is
> reached. Is there anything off-the-shelf that can do that?
>
> Thanks in advance
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190626/99fcc4fe/attachment.htm>
More information about the RE-Wrenches
mailing list