[RE-wrenches] need for outdoor DC disconnect

Kirk Herander vtsolar at icloud.com
Wed Jun 12 14:49:41 EDT 2019


All,

I am retrofitting an existing PV system with Storedge / LG Chem / optimizers
and updating some code issues. I am replacing the PVC conduit carrying the
array conductors into the building with metallic raceway to the point of DC
disconnect(i.e. the inverter).  The array is presently connected to an
Outback inverter / FM60 controller / AGM batteries (grid tied with backup).
If I am interpreting NEC 690.12 etc. correctly, a DC disconnect outdoors is
generally not required because of new rapid shutdown capability, amongst
other reasons. Would this be the case regardless of metal or plastic conduit
penetrating the building? The system at present has no outdoor DC disco, and
to me that's a violation in addition to lack of metallic raceway entering
the building. Thanks.

 

Kirk Herander

Owner|Principal, VT Solar, LLC 

Celebrating our 28th Anniversary 1991-2019

 
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com
&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aa
aaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B
%2BqtvcALkdDghvk4%3D&reserved=0> www.vermontsolarnow.com

dba Vermont Solar Engineering

NABCEPTM  2003 Inaugural Certificant

VT RE Incentive Program Partner

802.863.1202

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190612/44fcbf09/attachment.htm>


More information about the RE-Wrenches mailing list