I may have spoken too soon on this. It turns out that the LSOB system just
does not work with PV charge controllers. The Princeton Power Systems
DRI-10 inverter has charge controllers built in, which is why the system
was not working.
Cheers,
Dave
*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC
110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121* f. 607.277.2119
www.taitem.com
Solar • Sustainability • Energy • Design
B-Corporation Best for the World 2018 Honoree
On Thu, May 30, 2019 at 9:15 AM Dave Tedeyan <dtedeyan at taitem.com> wrote:
> Just a note about midnite's SOB rapid shutdown system. It does not seem to
> work with all inverters. I was recently helping someone with a Princeton
> Power Systems inverter add in rapid shutdown. There was some kind of line
> noise coming from the inverter that was causing the rapid shutdown system
> to not work at all. It held the string voltage down even when it should not
> have. The only way to get the string voltage back up was to physically
> disconnect the PV from the inverter. So we had to pull the rapid shutdown
> and will need to find another solution.
>
> Cheers,
> Dave
>
> *Dave Tedeyan, PE*
> Senior Engineer | Taitem Engineering, PC
>
> 110 South Albany Street | Ithaca, NY 14850
> o. *607.277.1118 x121* f. 607.277.2119
> www.taitem.com
>
> Solar • Sustainability • Energy • Design
> B-Corporation Best for the World 2018 Honoree
>
>
> On Wed, May 29, 2019 at 7:07 PM Rick Brown <
> rick at solshineenergyalternatives.com> wrote:
>
>> Jerry,
>>
>> Check out Midnight Solar’s Rapid Shutdown Shut Off Box (SOB).
>>
>> http://www.midnightsolar.com/
>>
>> rick brown
>> SolShine Energy Alternatives, LLC
>> Electrical & Solar Contracting Services
>> www.SolShineEnergyAlternatives.com
>> Check, Virginia 24072
>> 540.808.9502
>>
>> VA Class A Contractor Lic# 2705147660
>> VA Master Electrician Lic# 2710062762
>> VA Alternative Energy Systems Installer
>> NABCEP Certified PV Installation Professional 110112-21
>>
>> On May 29, 2019, at 5:44 PM, Jerry Caldwell <solarcowboy at yahoo.com>
>> wrote:
>>
>> Dear Wrenches,
>>
>> We are installing a system for a project we did not design. The plans
>> specify 5 Ginlong Solis inverters. Ginlong does not make their own rapid
>> shutdown device, so units by Innovative Solar Products have been specified.
>> The Innovative Solar rapid shutdowns are made to order and will take 4
>> weeks (not good for us).
>>
>> Does anyone know another mfr that makes rapid shutdown devices that are
>> compatible with other mfrs inverters?
>>
>> Thanks,
>>
>> Jerry Caldwell
>> Redwood Sun
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190530/0b9d3d6b/attachment.htm>
More information about the RE-Wrenches
mailing list