[RE-wrenches] 225A Meter Main with Pass Through Lugs

Jason Szumlanski jason at floridasolardesigngroup.com
Thu May 9 15:06:35 EDT 2019


Calc loads and see if you can replace the main with a 175A breaker if it
exists, or even 150A. This main breaker downsizing has been a go-to
exercise for us for existing meter-mains. It's frustrating being limited to
40A on the load side. That doesn't even get to 10kWdc with Enphase IQ7+,
which is becoming a pretty small system these days around here. I tell
every home builder I see to avoid meter-main combos but they keep putting
them in.

Sadly our utility accepts NONE of the "solar ready" panels on the market.
That's another snag we run into.


Jason Szumlanski
Florida Solar Design Group




On Thu, May 9, 2019 at 2:50 PM Sarah Ray <sarahmray at gmail.com> wrote:

> Hi Wrenches,
>
> Does anyone have a recommendation for a meter main with a 225A bus and
> pass through lugs? Eaton and SquareD make meter mains with a 225A bus, but
> no pass-through lugs, so they don't work well for most retrofit
> applications.
>
> We would like to connect our inverter output to a feeder that is fed by
> the pass through lugs in the existing 200A meter main (which is located at
> another building.) The inverter output has a 60A OCPD, so the 200A meter
> main bus is not sufficient.
>
> Any suggestions you have would be greatly appreciated!
>
> Thank you,
>
> Sarah Ray
>
> OnSite Energy, Inc.
> 619 N Church Ave, Suite 4
> Bozeman, MT 59715
> Cell: (406) 579-6512
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/0cdeafdb94296de805c0b8380e08649f56e19238?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=47934535e539a8f7>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/ef5390ae90b139898f6db1fa1928ac08f0792cf0?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5e1f020929d5c98c>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/cfb14dd7a433257700c74cdc0a2975faf0fd1870?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8073aec135156afc>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/d36e39964a6c24887a1376279695369b085573a3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=79fec82fea6a696f>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190509/f9aa748a/attachment.htm>


More information about the RE-Wrenches mailing list