Thu Apr 25 15:10:54 EDT 2019
Amos,
I have done this and it works. The VFX3524 will run a 3/4 HP (and a 1
HP) AC well pump just fine through a PSX-240. I have this setup in my
own home now, running on a 120V Magnum 4024AE. I would suggest a
soft-start AC pump with a conventional pressure switch, not the
constant-pressure approach. Add a 120VAC-coil single-pole relay on the
120V side, with the pressure switch wired to the relay's coil circuit
and the relay controlling the 120VAC between the inverter output and the
PSX-240 input, to eliminate the 12(?)W tare of the PSX-240. It'll work
fine and is completely reliable if professionally installed. We don't
need no stinking badges - er, Radians!
Allan at Sindelar Solar
On 4/25/2019 11:14 AM, Dave Angelini Offgrid Solar wrote:
>
> Time for a radian and lose the x240. Modernize the system to split
> phase and test for pressure leaks, pressure tank, pressure switch.
>
> My experience with the x240 got much better when Schneider, Outback
> went split phase. They are fine for solar people but one more headache
> to an offgrid homeowner. Good Luck!
>
> *Dave Angelini Offgrid Solar "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ e-mail offgridsolar at sti.net
> <mailto:offgridsolar at sti.net> text 209 813 0060*
>
> On Thu, 25 Apr 2019 09:50:12 -0700, "Andrew" <andrew at greenwired.com>
> wrote:
>
>> Hey Amos.
>>
>> It could be a multitude of things depending on what type of pump
>> motor it uses. Even if you get it fixed it's still got 10yr parts in
>> it elsewhere that will have to probably be replaced soon too. Have
>> you looked into the Grundfos SQF series? They are really nice, run
>> off AC or DC but are kind of limited to their flow rate at the range
>> I think the best you could get would be 12 gpm. That way he could run
>> the pump during the day off solar direct and then switch it over to
>> AC for evening pumping and cut down usage on his house system.
>>
>> Andrew Perkins
>>
>> Greenwired
>>
>> P: 707-923-2001 ext. 100
>>
>> 1150 #1 Evergreen Rd
>>
>> Redway, CA 95560
>>
>> www.greenwired.com
>>
>> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
>> *On Behalf Of *Amos Post
>> *Sent:* Thursday, April 25, 2019 9:22 AM
>> *To:* RE-wrenches
>> *Subject:* [RE-wrenches] Fwd: Well Pump Sizing
>>
>> I have an off-grid customer who is having problems with his 10 year+
>> old 1/2hp well pump. It is running and running at 900watts constant
>> and hardly building pressure and even caused the 250amp breaker on
>> his single VFX3524 inverter to trip. He is running the pump at 240V
>> off a x240 transformer and thinking he might need to replace the pump
>> and might want to go with a larger 3/4hp pump for better performance
>> and more future capacity. Does anyone have experience running 3/4hp
>> pumps on this setup? The pump is approx. 200' down in the well.
>>
>> *Amos Post*
>>
>> Integrity Energy
>>
>> O: 802.763.7023
>>
>> C: 802.291.2188
>>
>> <https://www.facebook.com/integrityenergyllp?ref=br_tf>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
--
*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*