[RE-wrenches] SMA Micro-grid

William Miller william at millersolar.com
Wed Apr 24 12:48:45 EDT 2019


Louis:

Thanks for the message. I’m a bit embarrassed that I misunderstood the start voltage significance. I modified the string wiring and system is operating. Thanks again!

William Miller

> On Apr 24, 2019, at 7:46 AM, <louis at solarcowboyz.com> <louis at solarcowboyz.com> wrote:
> 
> William,
> 
> The start voltage is 285v from what I see covered on the specifications in manual.
> Data sheets are not specifications, I have seen many a error on these over the years.
> 
> This voltage is way low regardless if the start voltage was 220v.
> By the time the PV voltage gets dragged down when finding the VMPP it is going to be down near the low end of the range anyway.
> 
> I always like to see the VMPP up near the top of the VMPP point(but not to high!).
> This means less current, which means less heat, which means longer life.
> 
> Looks like the is either a PV problem or a bad design in the first place.
> 
> Louis Segarra
> 
> 
> -------- Original Message --------
> Subject: Re: [RE-wrenches] SMA Micro-grid
> From: William Miller <william at millersolar.com>
> Date: Tue, April 23, 2019 11:40 am
> To: Harry Mahon <Michael.Mahon at sma-america.com>
> Cc: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> 
> Mike:
> 
> Thanks for the reply. Good information. 
> 
> The AC system is 208. The data sheet indicates that for 208 the PV startup is 220. Today we have 260 VDC. That should be enough!?
> 
> I checked EMT he AC frequency in case it was on shift mode. It is right at 60.00. 
> 
> Still in waiting mode. I had always thought “waiting” was for grid reconnect timeout...
> 
> William
> 
>> On Apr 23, 2019, at 8:47 AM, Harry Mahon <Michael.Mahon at sma-america.com> wrote:
>> 
>> William –
>> Waiting mode means the DC voltage is below the inverter start.  For SB 4000-12, that would be 285 VDC (and will work to 250VDC once that is hit).
>>  
>> If you knock on the inverter lid, the display will cycle and you will see the DC voltage displayed.
>>  
>> If the yellow LED is not on, this should not be an AC side issue.
>>  
>> I do not think the “Backup Mode” parameter would be the cause, but if the voltage check shows well above PVstart, it would be worth a call to service.  If the inverter was left in on grid mode, then it will work when the SI is creating a micro-grid with frequency within UL1741 limits.  If the system is off-grid, I would think the SB would have been set to off-grid mode rather than enabling Backup Mode to “on all” that allows switching from on-grid to off-grid parameter sets by RS485 command.
>>  
>> Best-
>> Mike
>>  
>> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of William Miller
>> Sent: Monday, April 22, 2019 6:54 PM
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> Subject: [RE-wrenches] SMA Micro-grid
>>  
>> Friends:
>>  
>> I am working on an AC coupled SMA system in an off-grid setting.  We have an SB4000-12 that was disconnected for a number of years and we reconnected it.  The inverter is stuck in the waiting mode and  will not generate power.  The Sunny Islands and Sunny Boys are connected via an RS485 communication system.
>>  
>> I suspect there is a programming step I have not yet accomplished.  I recall some years ago I programmed the other Sunny Boys for off-grid operation.  I can’t find anything in any of the manuals about how to check the programming.  I also suspect SAM tech support talked me through this and the information may not be published.
>>  
>> Does this ring a bell with any of you?  Any advice? 
>>  
>> Thanks in advance.
>>  
>> William Miller
>>  
>> Miller Solar
>> 17395 Oak Road, Atascadero, CA 93422
>> 805-438-5600
>> www.millersolar.com
>> CA Lic. 773985
>>  
>> Quote of the day:  “If there is a job you hate, get really,
>> really good at it. Maybe you will hate it less.“ W. Miller
>>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190424/ce8bc1c4/attachment.htm>


More information about the RE-Wrenches mailing list