[RE-wrenches] High altitude off-grid systems

Steve Higgins steve at surrette.com
Fri Apr 12 11:17:20 EDT 2019


Not to add fuel to the fire... and it's been almost 7 years since I've been
with an Inverter manufacturer so here is my .02 cents...  So again, I hope
I'm not overstepping the boundaries of the Wrenches list.

If I remember correctly the main issue with the high altitude installs are
some of the components that are used to build the inverter/controllers
aren't rated to be used at high altitude, one of the main components that
have this issue is the electrolytic capacitors.    Of course, the specs
vary from component to component.   I've seen some rated as low as 8000 ft
to some as rated as high as 30,000 ft.   It really just depends on the
part(s) that the manufacturer used to build the product.

As you gain altitude the temperatures and the air pressure decrease, as it
was explained to me years ago the problem is with the temperature decrease,
this will affect the capacitance of the capacitor.  The colder temps will
reduce the overall capacitance of the capacitor, just like it will with a
battery.

These caps are generally used to filter noise from circuits, so when these
fail, or the capacitance values fall, you don't get the filtering you need
and this induces noise into your circuitry possibly causing overall failure
or worse,  the dreaded intermittent failure.   Generally, if the
inverters/controllers are kept on and warm, you won't have too many
problems, it's when they are in extremely cold temperatures is when you
will start having issues.

Hope this helps!   Have a good weekend!


<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020  m +1.206.790.5840
f +1.902.597.8447  e steve at surrette.com
<#SignatureSanitizer_> <http://www.facebook.com/RollsBattery>
<http://www.facebook.com/RollsBattery> <http://www.twitter.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------


On Fri, Apr 12, 2019 at 7:47 AM <chris at oasismontana.com> wrote:

> Folks:
>
>
>
> The issue here ulltimately isn’t whether it works or not, it’s if it’s
> WARRANTED.  Some purchasers (in this case the USFS) mandate that all
> equipment be warranted for high altitudes.  And that leaves out several
> major suppliers.
>
>
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Ray
> *Sent:* Thursday, April 11, 2019 10:55 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] High altitude off-grid systems
>
>
>
> We've had some systems at 11,000 ft plus, for almost 20 years.  We have
> mixtures of Outback, Midnite, Blue Sky, and old Trace equipment.  Never any
> issues with electronics related to altitude.  Actually the altitude related
> system issues are generator derating, and array output exceeding STC
> ratings on really clear cold days due to the thin atmosphere.  The third
> issue would be installers not being able to catch our breath after jogging
> back to the truck.
>
> Ray Walters
>
> Remote Solar
>
> 303 505-8760
>
> On 4/11/19 3:39 PM, Dan Fink wrote:
>
> Hi Chris; I am deeply concerned about this as nearly 100% of the systems I
> install are at 8000 ft (2500m) or higher. I've never had a problem with
> warranty claims to Outback or Schneider up to this time. If this is a "new
> thing" I'd really like to know about it, on list or off.
>
>
>
> The alitude de-rate stuff seems to involve dialectric ratings on the
> transformer coils, and low air density for cooling. I think that's all in
> ANSI.
>
>
>
>
> Dan Fink
>
> Director of Solar Education, Greendustrial Training LLC
>
> IREC Certified Instructor™ for:
>
> ~ PV Installation Professional
>
> ~ Small Wind Installer
>
> NABCEP PV Associate
>
> Executive Director, Buckville Energy Consulting
>
> NABCEP Registered Continuing Education Providers
>
> dan.fink at greendustrialtraining.com
>
> 970-672-4342
>
>
>
>
>
>
>
>
> On Thu, Apr 11, 2019 at 1:28 PM <chris at oasismontana.com> wrote:
>
> Hi folks:
>
>
>
> I am curious as to how many of you sell/install battery/inverter systems
> at high altitudes?  Have you had any particular issues with them?  Last
> year we discovered (in a mostly costly fashion) that Schneider inverters
> (and also Outback) are not warranted above 6500 ft.
>
>
>
> Magnum inverters are warranted to 15,000 ft max altitude.
>
>
>
> Best,
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
> 406-777-4309 or 4321
>
> 406-777-4309 fax
>
> www.oasismontana.com
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
>
> List sponsored by Redwood Alliance
>
>
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
>
>
> Change listserver email address & settings:
>
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>
>
> List rules & etiquette:
>
> www.re-wrenches.org/etiquette.htm
>
>
>
> Check out or update participant bios:
>
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190412/5ace708f/attachment.htm>


More information about the RE-Wrenches mailing list