[RE-wrenches] HV Module Testing

Brian Mehalic brian at solarenergy.org
Wed Apr 10 18:51:42 EDT 2019


The IEC 62446 standard for IRT on PV is:

Voc at STC x 1.25 = 120 V to  ≤ 500 V, test to 500 V
Voc at STC x 1.25 = > 500 V, test to 1,000 V

They specify using one of two methods:

1. With the array short circuited (a la the Seaward test meter style)

2. Testing both positive and negative to ground - both the negative and
positive leads need to be isolated (fuse open/breaker off, and disconnected
from parallel busbar connections).  In my experience, putting the meter in
series (meter positive to PV negative, meter negative to ground) is usually
sufficient for finding ground-faults.

Make sure the meter-to-ground connection is low resistance, and that the
connection point is something that is actually bonded to the equipment
grounding system.

Temperature, humidity, and the amount of "glass" being tested will have
significant impacts on measured results, but you're really looking for an
outlier, assuming it isn't a hard fault that could've been found with a DMM
or a visual inspection.

Always a good idea to check with the module manufacturer to see if they
have documentation on their recommended procedure.

Cheers,

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Wed, Apr 10, 2019 at 3:07 PM <drake.chamberlin at redwoodalliance.org>
wrote:

> That is very helpful. If I do the high voltage test, can I test from both
> positive to the frame and negative to the frame?
>
> Thanks,
>
> Drake
>
>
>
> ----- Original Message -----
> From:
> "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>
> To:
> "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Cc:
>
> Sent:
> Wed, 10 Apr 2019 10:35:50 -0700
> Subject:
> Re: [RE-wrenches] HV Module Testing
>
>
> Drake
> I have performed test for manufactures and you must keep the test voltage
> under the max rated voltage of the module, we have a bunch of tests we do
> but in short, you need to see the modules up close, look at the edges and
> back sheets look for green, brown or black spots, you need to do testing
> both dry first then wet if it is a ground fault concern. Most of the time
> the visual will find the issues but you still want to verify what you think
> you see. Make sure you look at the wiring to and from, the combiner box(s)
> or even the inverter(s).
>
> On Wed, Apr 10, 2019 at 8:31 AM Drake <
> drake.chamberlin at redwoodalliance.org> wrote:
>
>> Hello Wrenches,
>>
>> We are troubleshooting an array of Orion modules, either 230s or 250s.
>> The array is showing a ground fault.
>>
>> We would like to test these modules with an insulation tester?
>>
>> We would like to apply 500 V or 1000 V to each the + and – and test
>> resistance to ground.
>>
>> Is this practice safe for individual PV modules? Is there anything I
>> should be aware of before attempting this?
>>
>> Thanks,
>>
>> Drake
>>
>> Drake Chamberlin
>>
>>
>>
>>
>>
>> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
>> Solar PV 740-448-7328*http://athens-electric.com/
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190410/a6eb9efb/attachment.htm>


More information about the RE-Wrenches mailing list