Hello Wrenches
We have a project taking a 480kw carport array feeding a Satcon 500kw
inverter and upgrading it to 8- 50 kw SMA inverters.   The SW 285's, in
strings of 12, are combined in groups of 8 in the field then fed to the
inverter DC input. In my experience SMA sells a rapid shutdown box with 4
inputs but only 2 outputs to pair with their Inverters that have 3 MPPT
channels and they instruct you to combine the strings at the rapid shutdown
box on the roof then install a pigtail on that wire at the inverter
splitting it into two and sending the output of those two combined strings
into two seperate MPPT channels.  We would like to do the same with
combiner panels in reverse. I spoke with SMA and they are checking with
Germany but I knew I would find info here.  Anyone with experience with
this?

-- 
Gary Easton