[RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

Rich Nicol rich at solartechvt.com
Mon Apr 1 12:32:43 EDT 2019


Thanks for the feedback and pointers, its greatly appreciated – I checked frequency and it was spot on at 60Hz but with minimal decimal places on my meter. 

This must be something new with Magnum as I haven’t seen the voltage issues on other systems nor have I had any issues with appliances or clocks etc. 

I hate to admit that I seem to find myself in constant frustration for one reason or another with the primary suppliers of offgrid system components!

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Monday, April 1, 2019 10:58 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

 

Rich, this is a known flaw in the Magnum AE and PAE series. I have one longtime client for whom I supplied a 4448AE around 2009 who later told me that had he known of this frequency issue he wouldn’t have selected Magnum. 

Allan Sindelar 


On Apr 1, 2019, at 6:56 AM, Christopher Warfel <cwarfel at entech-engineering.com> wrote:

I would think it has to be frequency. What else could shift the time?  Up until about 2 years ago we were a grid isolated system and no one could use a plug in the wall clock. It takes just a very little off 60 Hz for a clock to keep incorrect time. Being off .5 Hz will result in 42,300 cycles in one day. When I worked in power plants the frequency was a digital display to the 6th place I think. The operator said if that decimal place was off by more than 2 from ISONE, it would trip off line. The steam turbines would be destroyed otherwise. Chris

On 4/1/2019 7:08 AM, Rich Nicol wrote:

Hello Wrenches

I have a site with two PAE 48v Magnum inverters stacked. System voltage fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split on the two lines.

Site has a few electrical peculiarities I haven’t seen on the many other sites I have with Magnum inverters. Among those is three digital clocks on appliances that lose ~ 5 min per day consistently. A forth clock which is on a weather station with a transformer where it plugs into a receptacle keeps time and of course the computers do as they are web connected. 

I checked all neutral connections and verified proper N-G bond.

All connections appropriately torqued.

My recollection is the modest voltage swings are within Magnum spec. But its constantly moving about which seems somewhat suspect to me.

Any suggestions?

Thanks

RIch





_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190401/b5189307/attachment.htm>


More information about the RE-Wrenches mailing list