[RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

Jason Szumlanski jason at floridasolardesigngroup.com
Mon Apr 1 06:38:59 EDT 2019


DC Coupled, but solar is disabled at this time.

I haven't been back to the site, but I plan to test each inverter
individually with the other three chargers disabled to see if there is one
offender.





On Sat, Mar 30, 2019 at 3:47 PM Kienan Maxfield <maxfieldsolar at hotmail.com>
wrote:

> Jason,
>
> This isn’t an AC coupled system is it? There is a very common issue that
> can occur when you AC couple XWs on lithium batteries.
>
> If this is AC coupled, I’ll go into more detail on what I think your
> problem might be. Also, let us know if you got it fixed.
>
> Thanks,
> Kienan
> maxfieldsolar at hotmail.com
> (801) 631-5584
>
>
>
> On Mar 27, 2019, at 9:42 AM, Sandra Herrera <Sandra.Herrera at se.com> wrote:
>
> Jason,
>
>
>
> Lets connect off-list direct email, I will need to send you a file.
>
>
>
> Also, this can only be done using the Cofig Tool.
>
>
>
> Sandra.herrera at se.com
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski
> *Sent:* Wednesday, March 27, 2019 8:32 AM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints
>
>
>
> [External email: Use caution with links and attachments]
> ------------------------------
>
>
>
> I can't even get 1 hour of charging. The voltage rises too quickly and the
> battery management systems disconnect the battery.
>
>
>
> What is the calibration process?
>
>
>
> I still plan to disable the chargers that are reporting the wrong (lower)
> voltage and see if the others (individually) still ignore the setpoints.
> It's a very remote location, so diagnostics are extremely difficult.
>
>
>
>
>
>
>
>
>
>
>
> On Tue, Mar 26, 2019 at 9:00 AM Sandra Herrera <Sandra.Herrera at se.com>
> wrote:
>
> Jason,
>
>
>
> The Battery daily summary from the ComBox is information on one day at a
> time, this is not part of the logs, and it should be available even if you
> have 1 hour or charging.
>
>
>
> However, based on your discovery of different DC voltages from the
> inverter, my recommendation is to calibrate them.
>
>
>
> Sandra
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski
> *Sent:* Monday, March 25, 2019 4:18 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints
>
>
>
> [External email: Use caution with links and attachments]
> ------------------------------
>
>
>
> This is a newly commissioned Lithionic LiPo battery on an old system that
> has been out of commission for over a year. 51V nominal battery. Logs are
> not possible. This happens within minutes of bulk charging initiation.
> There is no spike. It's a steady rise.
>
>
>
> Jason
>
>
>
>
>
>
>
>
>
>
>
> On Mon, Mar 25, 2019 at 4:41 PM Sandra Herrera <Sandra.Herrera at se.com>
> wrote:
>
> Jason,
>
>
>
> Can you share the Battery Daily Summary from the ComBox? Only select the
> battery voltage so it is easier to see where the 0.8V jump is occurring.
>
>
>
> Also, what battery are you using?
>
>
>
> Thanks
>
>
>
> Sandra Herrera
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jason Szumlanski
> *Sent:* Monday, March 25, 2019 1:36 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints
>
>
>
> [External email: Use caution with links and attachments]
> ------------------------------
>
>
>
> I have four inverter/chargers (master and 3 slaves) that are blowing past
> their 57.6V setpoint that I programmed and confirmed via the Context
> Combox. They are hitting 58.4V and tripping the battery management units on
> a set of Lithium Batts. Any ideas why this would happen? I can disable
> chargers on individual units, so I know the settings are getting uploaded
> via the Combox.
>
>
>
> Jason Szumlanski
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/26113f0e95b929bf18000dae50227bf70b956108?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F18cba8599d23d6d99bcbe44f3ec46d60f0c4d90e%253Furl%253Dhttps%25253A%25252F%25252Feur02.safelinks.protection.outlook.com%25252F%25253Furl%25253Dhttps%2525253A%2525252F%2525252Fmailtrack.io%2525252Ftrace%2525252Flink%2525252F8d9e12ac10c579b7810fd6e15594017b4395543d%2525253Furl%2525253Dhttp%252525253A%252525252F%252525252Flists.re-wrenches.org%252525252Foptions.cgi%252525252Fre-wrenches-re-wrenches.org%25252526userId%2525253D1613865%25252526signature%2525253Dff64cebca7b2a8fe%252526data%25253D02%2525257C01%2525257Csandra.herrera%25252540se.com%2525257C29357b33ca254f5c0b0508d6b1781e9c%2525257C6e51e1adc54b4b39b5980ffe9ae68fef%2525257C0%2525257C0%2525257C636891526800151601%252526sdata%25253Dej4W%2525252FA0RbNrDhRy5Y%2525252FU4rx6NEPf87CEOBUTInVUMfq4%2525253D%252526reserved%25253D0%2526userId%253D1613865%2526signature%253Db1ee2a5091a592df%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595675889%26sdata%3DVZgn%252BYgLWYwy8tNVgSfqpri7OidwjWTVl8CyxTni7f4%253D%26reserved%3D0&userId=1613865&signature=f5f762027d04770e>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2Fe28e6a185e7da9eaa3d1dc625605218dc2cc373d%3Furl%3Dhttp%253A%252F%252Fwww.mail-archive.com%252Fre-wrenches%2540lists.re-wrenches.org%252Fmaillist.html%26userId%3D1613865%26signature%3D0b2c152acef4d3a8&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595685894&sdata=3X3itC8zZ3hT1ziCwU%2FqVIgsb149C4N5QUYI2bFqEyk%3D&reserved=0>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/40625297542e8e4b29528f24722efbe2fd09154b?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F7a33632c4c87da9837c960e385230c617a913cb8%253Furl%253Dhttps%25253A%25252F%25252Feur02.safelinks.protection.outlook.com%25252F%25253Furl%25253Dhttps%2525253A%2525252F%2525252Fmailtrack.io%2525252Ftrace%2525252Flink%2525252F58c2621c30bb36ba8f1b7bc660c2029c0d7b170d%2525253Furl%2525253Dhttp%252525253A%252525252F%252525252Fwww.re-wrenches.org%252525252Fetiquette.htm%25252526userId%2525253D1613865%25252526signature%2525253D43f1391ecbe9e76f%252526data%25253D02%2525257C01%2525257Csandra.herrera%25252540se.com%2525257C29357b33ca254f5c0b0508d6b1781e9c%2525257C6e51e1adc54b4b39b5980ffe9ae68fef%2525257C0%2525257C0%2525257C636891526800161610%252526sdata%25253DiymCQe2Js%2525252BbEuTPZxj3qtQX%2525252FuIFDsiF0AabIXSIsh0k%2525253D%252526reserved%25253D0%2526userId%253D1613865%2526signature%253D62e3763c879d975f%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595695903%26sdata%3Ds0rqr7uz7fna2QYgshZM7f3g5uEXbQ2OWKGhrbdhASI%253D%26reserved%3D0&userId=1613865&signature=33fa7765f5fa9b2b>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/c94c641266b9f665380b0f77f82189404c0a8343?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F5e5882bdb74c6623d91159977445cccc4f582319%253Furl%253Dhttps%25253A%25252F%25252Feur02.safelinks.protection.outlook.com%25252F%25253Furl%25253Dhttps%2525253A%2525252F%2525252Fmailtrack.io%2525252Ftrace%2525252Flink%2525252F9bc2e78bed9b8b94e220a1d9572411cd56c6863b%2525253Furl%2525253Dhttp%252525253A%252525252F%252525252Fwww.members.re-wrenches.org%25252526userId%2525253D1613865%25252526signature%2525253D9e6fdef31370bf88%252526data%25253D02%2525257C01%2525257Csandra.herrera%25252540se.com%2525257C29357b33ca254f5c0b0508d6b1781e9c%2525257C6e51e1adc54b4b39b5980ffe9ae68fef%2525257C0%2525257C0%2525257C636891526800171614%252526sdata%25253D4W%2525252Ft2RLvs9Uwv2dfgyjW%2525252BzAC%2525252BtWUX7HoN9BNAvMv3wA%2525253D%252526reserved%25253D0%2526userId%253D1613865%2526signature%253Da11ac01d03fd1498%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595695903%26sdata%3DQlHASRXR69AVP542BIYea1B0mJ%252Be9H1pWNKBdyd5gvM%253D%26reserved%3D0&userId=1613865&signature=cbc97f1dfe904f7b>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/5bd2b3aa83e1f96da4f02153cfa771a08e023192?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F472d17d9be91574dff6d989a837c993215540b7c%253Furl%253Dhttp%25253A%25252F%25252Flists.re-wrenches.org%25252Foptions.cgi%25252Fre-wrenches-re-wrenches.org%2526userId%253D1613865%2526signature%253D1ff79895c955d6d1%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595705917%26sdata%3D7KZZSUXAlGw%252FWXKB5McplMwYlqp9G7anFf3MnHCSCDU%253D%26reserved%3D0&userId=1613865&signature=8e34d7004bad0104>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fmailtrack.io%2Ftrace%2Flink%2F62e382fbba22bd0322ed491c70013122b32ac337%3Furl%3Dhttp%253A%252F%252Fwww.mail-archive.com%252Fre-wrenches%2540lists.re-wrenches.org%252Fmaillist.html%26userId%3D1613865%26signature%3D459f1c55a0251f6b&data=02%7C01%7Csandra.herrera%40se.com%7C090af5434b7c4c0bd91a08d6b2c97154%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892975595715918&sdata=HFPYSGtnqmI4WJDKqpLTTFJTTPTXXvKVbPhK4DtaU7A%3D&reserved=0>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/f19f06ec2ae160387682243afdc7b72031b5fb21?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F6ccc977170ec9afe7ae227149fe1b7e48fcad269%253Furl%253Dhttp%25253A%25252F%25252Fwww.re-wrenches.org%25252Fetiquette.htm%2526userId%253D1613865%2526signature%253D97660bec94e18d53%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595715918%26sdata%3DGRpNhIC6OIVxOkt2J3fA4PULlAuO0CHVLwWfv6QkxIo%253D%26reserved%3D0&userId=1613865&signature=fb6be45118537ca1>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/68cb26453b505327ea58091de02a15b2384d6bda?url=https%3A%2F%2Feur02.safelinks.protection.outlook.com%2F%3Furl%3Dhttps%253A%252F%252Fmailtrack.io%252Ftrace%252Flink%252F73257c2326046c73eafa7a859ff008b50d628ba7%253Furl%253Dhttp%25253A%25252F%25252Fwww.members.re-wrenches.org%2526userId%253D1613865%2526signature%253D505b9f731c70e5e6%26data%3D02%257C01%257Csandra.herrera%2540se.com%257C090af5434b7c4c0bd91a08d6b2c97154%257C6e51e1adc54b4b39b5980ffe9ae68fef%257C0%257C0%257C636892975595725923%26sdata%3DDd2hHbwJAtEDIzBWNGLjYIddAOB2QL7%252BP4xZc%252Flr%252FZ0%253D%26reserved%3D0&userId=1613865&signature=dd33ba8ed0ce79a7>
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/fb286390fc1842673c0a1e4d3c693782c4b207ac?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=223403ff68d4861f>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/296bed90735643491cb4c826c3d29d9e8ef04476?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=52942c76fbe9d5ca>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/b432ba883ab512ecd6207e2b3c4414d3d5b9ff57?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=fef0819dc8606d03>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/fb286390fc1842673c0a1e4d3c693782c4b207ac?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=223403ff68d4861f>
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <https://mailtrack.io/trace/link/289dbc9e853760af0718d6f48af83bd750d05875?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1bdeeb6f36bcb210>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/296bed90735643491cb4c826c3d29d9e8ef04476?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=52942c76fbe9d5ca>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/caf461f31741c95f9aff285059b1204dedcaa3ce?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=3298446c8cf2d713>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190401/3369916a/attachment.htm>


More information about the RE-Wrenches mailing list