[RE-wrenches] Enphase Envoy in PVC J-Box

Christopher Warfel cwarfel at entech-engineering.com
Thu Mar 28 14:43:04 EDT 2019


If you are using the IQ Combiner, the wiring diagram is on the inside 
cover.  Coming from the array, L1, L2 and G. Going to the utility 
interconnection, L1, L2, G, N.  L1, L2 into the 20a breakers, G to the G 
busbar, N to the N busbar.  It's all there and is a nice package I 
think.  My personal preference is to use manufacturer's equipment 
instead of making my own. I don't know if the AHJ would complain about 
non-listed equipment in the case of making your own DAS center. The 
Envoy may need a button pushed once in a while.  I have asked customers 
to do this to save a trip. The Enphase "package" is safe for them to do 
that.  I hope I did not miss your question. Chris

On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
> When mounting an Envoy on the supplied DIN rail in a PVC box wired via 
> PVC conduit, is there any requirement to accompany the conductors with 
> a ground wire? The envoy itself does not have a ground connection and 
> the only exposed metallic part is the DIN rail.
>
> I'm thinking I need to mount a ground lug in the PVC box so the 
> circuit conductors have a ground wire in the conduit. I have always 
> used the IQ combiner even for larger systems because it was just 
> easier. I'm considering changing to a regular PVC junction box with 
> just an Envoy.
>
> While on the subject, if there is ample space within a load center, 
> would it be permissible to mount the Envoy right inside the enclosure? 
> 400A plus load centers in residential settings often have a lot of 
> empty space!
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190328/e3373117/attachment.htm>


More information about the RE-Wrenches mailing list