Hello, the generator transfer switches work as you request, however the
ones that I have used require the generator start battery 12-volt
connection to pull the transfer switch. You may have to provide a 12-volt
source to accomplish this transfer. The last ones I used were from Eaton,
Generac, and others, all using a 12-volt to activate the transfer
On Tue, Mar 19, 2019 at 9:54 AM Mac Lewis <maclewis1 at gmail.com> wrote:
> Hello Wrenches,
>
> Does anyone have experience with a 200A outdoor transfer switch that will
> automatically seek voltage? Meaning that if priority voltage source (grid)
> isn't available and second source is available it will switch to it with no
> external communication? We are trying to do a whole house backup, and
> critical load panel isn't possible. This may be common, I just haven't
> done it.
>
> Thanks in advance
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190319/6a3311ab/attachment.htm>
More information about the RE-Wrenches
mailing list