Christopher Warfel cwarfel at entech-engineering.com
Mon Feb 25 17:59:11 EST 2019


Yes, microinverters and now I would think other typologies will be 
included with module level disconnects becoming more common and I guess 
required. So, as long as you can disconnect each non microinverter 
individually, and microinverter strings by one disconnect, you should 
meeting the intent.  Labeling is key too. I still think that this was a 
big error and the stated intention of making rooftop pv safer has not 
been achieved.  The wheel fell off of this "safety improvement". 
Technology is catching up though. Anyone on a roof better assume the 
array is live until proven otherwise no matter what installation type it 
is. Chris

On 2/25/2019 5:45 PM, Rebekah Hren wrote:
> I should follow up to say that yes Chris is correct - each inverter 
> does require its own equipment disconnects (AC and DC) per 690.15, but 
> those can be connectors, like for Enphase, or any number of other 
> things, as detailed in 690.15. If you try to keep system and equipment 
> disconnect rules separate in your mind, I think it helps - although of 
> course the inverter AC disconnect for a string inverter will often 
> also be serving as the system disconnect, so there is a lot of overlap.
>
>
> On Mon, Feb 25, 2019 at 5:39 PM Rebekah Hren <rebekah.hren at gmail.com 
> <mailto:rebekah.hren at gmail.com>> wrote:
>
>     Hi Chris and William
>     There was certainly no intention to mandate that all inverters
>     connect to one OCPD/disconnect.But 705.12(B)(1) in 2017 clarifies
>     that systems like Enphase could have multiple inverters on one
>     breaker, certainly not  that all inverters in a building have to
>     be on breaker.
>
>     If an AHJ raises this issue the answer is as follows:
>
>     A single inverter can be called a single PV system  - see the
>     diagrams in 690.1(b). A building can have multiple PV systems per
>     690.4(D).
>
>     Each PV system can have no more than 6 system disconnect switches
>     per 690.13(D). Circuit breakers are allowed as PV system
>     disconnects - 690.13(F)(1).
>
>     There is no limit to the number of PV systems allowed on a building.
>
>     Therefore, each inverter can be connected to its own breaker/disco
>     for that PV system.
>
>
>     A few further comments :
>
>     A single PV system can have a single inverter, or multiple
>     inverters. It is up to you to define the system and the PV system
>     disconnect(s) associated with it.
>
>     OR multiple inverters (power sources) can be connected to a single
>     OCPD/disco up to the manufacturer's maximum OCPD limit, per
>     705.12(B)(1).
>
>     OR multiple (let's say 10) inverters in a single system can each
>     have their own OCPD/disco and ONE master PV system disconnect for
>     all 10 inverters to follow the fules of 690.13(D).
>
>
>     Lots of options, all allowed!
>
>
>     Best,
>
>     Rebekah
>
>     Principal, CMP-4
>
>
>     On Mon, Feb 25, 2019 at 5:31 PM Christopher Warfel
>     <cwarfel at entech-engineering.com
>     <mailto:cwarfel at entech-engineering.com>> wrote:
>
>         Just reading more slowly, each inverter has to be on its on
>         separate disconnect means. You cannot put multiple inverters
>         on the same disconnecting means unless there are individual
>         disconnecting means upstream.
>
>         On 2/25/2019 10:53 AM, William Miller wrote:
>>
>>         Friends:
>>
>>         I have an NEC code question on an upcoming project.  It is a
>>         home that has an existing 8 kW ground-mounted grid-tied
>>         system.  The owner wants to add another 10 kW of grid-tied
>>         PV.  My question is about 705.12, point of connection.
>>         Specifically section (D)(1).  That section states:
>>
>>         /The source interconnection of one or more inverters
>>         installed in one system shall be made at a dedicated circuit
>>         breaker or fusible disconnecting means./
>>
>>         So if there are going to be two inverters on premise, do the
>>         outputs have to be aggregated to connect via one circuit
>>         breaker?  This might be difficult to do as the exiting
>>         inverter is connected via a different sub-panel than the one
>>         that is planned to receive the new inverter output.
>>
>>         This article
>>         <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/>
>>         addresses the question.
>>
>>         I would be very grateful if any of you can share any
>>         experience you might have in interpreting this section of the
>>         code.
>>
>>         Thanks in advance.
>>
>>         William
>>
>>
>>         _______________________________________________
>>         List sponsored by Redwood Alliance
>>
>>         List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>         Change listserver email address & settings:
>>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>         List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>         List rules & etiquette:
>>         www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>
>>         Check out or update participant bios:
>>         www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>
>         -- 
>                                 Christopher Warfel
>              ENTECH Engineering, Inc.
>         PO Box 871, Block Island, RI 02807
>             401-466-8978
>         <http://entech-engineering.com>
>
>
>         _______________________________________________
>         List sponsored by Redwood Alliance
>
>         List Address: RE-wrenches at lists.re-wrenches.org
>         <mailto:RE-wrenches at lists.re-wrenches.org>
>
>         Change listserver email address & settings:
>         http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>         List-Archive:
>         http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>         List rules & etiquette:
>         www.re-wrenches.org/etiquette.htm
>         <http://www.re-wrenches.org/etiquette.htm>
>
>         Check out or update participant bios:
>         www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>     -- 
>     Tel: 336.266.8800
>     NABCEP Certified Solar PV Installation Professional™ 091209-85
>     NC Licensed Electrical Contractor
>
>
>
> -- 
> Tel: 336.266.8800
> NABCEP Certified Solar PV Installation Professional™ 091209-85
> NC Licensed Electrical Contractor
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/815fef1d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/815fef1d/attachment.jpg>


More information about the RE-Wrenches mailing list