[RE-wrenches] Multiple inverters

Christopher Warfel cwarfel at entech-engineering.com
Mon Feb 25 17:23:27 EST 2019


We just did this, and I think as long as each disconnecting means refers 
to the other multiple sources and their location, and the directory 
refers these multiple sources, you are compliant with NEC2017.

I guess I will find out.....

Chris



On 2/25/2019 12:07 PM, August Goers wrote:
> Hi William -
>
> In this case, it is helpful to look forward to the 2017 NEC for guidance:
>
> image.png
>
> I believe it's perfectly fine to have multiple inverter breakers in 
> your main.
>
> August
> Luminalt
>
>
> On Mon, Feb 25, 2019 at 8:42 AM William Miller 
> <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>
>     Friends:
>
>     I have an NEC code question on an upcoming project.  It is a home
>     that has an existing 8 kW ground-mounted grid-tied system.  The
>     owner wants to add another 10 kW of grid-tied PV.  My question is
>     about 705.12, point of connection.  Specifically section (D)(1).
>     That section states:
>
>     /The source interconnection of one or more inverters installed in
>     one system shall be made at a dedicated circuit breaker or fusible
>     disconnecting means./
>
>     So if there are going to be two inverters on premise, do the
>     outputs have to be aggregated to connect via one circuit breaker? 
>     This might be difficult to do as the exiting inverter is connected
>     via a different sub-panel than the one that is planned to receive
>     the new inverter output.
>
>     This article
>     <https://iaeimagazine.org/magazine/2014/01/16/load-side-pv-connections/>
>     addresses the question.
>
>     I would be very grateful if any of you can share any experience
>     you might have in interpreting this section of the code.
>
>     Thanks in advance.
>
>     William
>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-- 
             Christopher Warfel
                      ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                 401-466-8978
<http://entech-engineering.com>


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/d057a0c2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: bfekpgcofgbgfoai.png
Type: image/png
Size: 13146 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/d057a0c2/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: mehmhgglcfkiigdf.png
Type: image/png
Size: 45716 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/d057a0c2/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 109904 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/d057a0c2/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190225/d057a0c2/attachment.jpg>


More information about the RE-Wrenches mailing list