Hi William,
I did something like this but smaller so I do know it is possible. Along
with Outback I would look at the XW pro that is really made for a micro
grid.
Here is a link.
https://solar.schneider-electric.com/product/conext-xw-pro-na-solar-inverter/
I am testing it here for Schneider and here is a few screen shots of the
monitor Insight 2.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
> Colleagues:
>
>
>
> I have an interesting project. I am working for a family that lives part
> time in a planned community built some years ago. The HOA owns the 12 KV
> distribution and it is old and undersized. This client shares a 25 kVA
> transformer with a neighbor. This calculates out to 50 amps per home at
> 240 VAC.
>
>
>
> The client has more stuff to power than they have power. To make it
> possible to power their loads, I am imagining a pseudo off-grid
> installation. We have grid power, but precious little of it, so we have to
> stand-alone, at least to some degree.
>
>
>
> I am thinking that we can provide a battery inverter system that can be
> programmed to limit the draw from the grid. All the loads will be
> connected to the AC output of the inverter system. If the load increases
> over that programmed limit, a smart inverter system should be able to
> synchronize to the grid input and assist with inverted power (like gen
> support on the grid input). I believe the Radian inverters can do this.
>
>
>
> If occasionally the batteries get low, a generator can run intermittently
> and top off the batteries.
>
>
>
> There is an 8kW grid-tied system on site. This should be able to help
> power on-site loads or charge the batteries during day-light hours. I
> will
> specify a contactor to kill the GT feed if the grid goes out and the
> batteries are fully charged.
>
>
>
> We can add another 11 kW of GT solar. However, I am concerned that we
> might be over-feeding the transformer on sunny days. The neighbor has
> about 8 kW of GT solar. If you add all of the GT solar into this one 25
> kVA transformer, you arrive at 27 kVA. This is too much. Our additional
> GT solar might be with a Solar Edge HD-Wave SE10000-US. This inverter has
> an external box that can monitor net back-feed and limit the output of the
> SE inverter to a programmed level.
>
>
>
> Anyway, this is a lot of detail that maybe you donât need to know. My
> question is this: How would you design a system to take 12 kVA from a
> grid
> source and turn it in to 60, or more?
>
>
>
> Any input is appreciated.
>
>
>
> William Miller
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1a.PNG
Type: image/png
Size: 68740 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190209/e4543a3e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 2.PNG
Type: image/png
Size: 58706 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190209/e4543a3e/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 3.PNG
Type: image/png
Size: 226619 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20190209/e4543a3e/attachment-0002.png>
More information about the RE-Wrenches
mailing list