[RE-wrenches] Interesting gen start problem
William Miller
william at millersolar.com
Thu Dec 13 15:11:53 EST 2018
Friends:
While I’d like to think I have seen everything, I came across this scenario
recently that surprised me:
We replace an existing FX system that had a generator component. Since the
FX inverter can only provide 12 volts for generator start, and we did not
see a relay in the power room, we assumed there was a 12 volt coil relay in
the generator room. Turns out this was not the case.
Generators use the cranking battery voltage (B+) to power control
circuits. The B+ to start control relays is completed by a contact
closure. In this case, there was no relay. Instead the original installer
use the 12 volts from the FX inverters to provide substitute B+ to the
generator control circuitry.
The end result is we burned up the Radian control board. Apparently the FX
inverter had enough 12 volt capability to make this work, but the Radians
did not.
When we began troubleshooting, our first clue something was wrong was that
there was no relay. Our second clue was that one of the12 volt start leads
was grounded. We also burned up a relay in the generator.
I hope this little cautionary tale helps one of you avoid a burned up
control board someday, somewhere. This problem was a big headache.
William
PS: Here is a web page
<http://www.millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/TT-Radian/TT_Radian.html>
on this particular installation. On this project we incorporated some of
the GSLC wiring innovations discussed in this forum.
Wm
[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181213/cc285ce8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1803 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181213/cc285ce8/attachment.jpg>
More information about the RE-Wrenches
mailing list