[RE-wrenches] mate 3s locking
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Mon Nov 19 16:25:00 EST 2018
The SCP does not have extensive logging and can't tell you too much.
With Combox you can specify dozens of logs and the screen shot would tell
you why the genset did not start. There is improved xanbus firmware to help
with the limitations of the network. Once it is working I have found it
very reliable. I require the combox for my clients even if they do not use
it. The new Conext Gateway brings the whole system up to date with wifi
communication.
I have simple XW power systems with the same firmware that
came with the gear back 2007. Sorry, but very little experience with either
Outback or Schneider in grid-tie
Dave Angelini Offgrid Solar
"we go where
powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridsolar at sti.net [2]
text 209 813 0060
Mon, 19 Nov 2018 08:22:32
-0800, William Miller wrote:
Friends:
We installed XW systems up
until a few years ago and had problems similar to those with Outback but
subtly different. Here is a short list of some of our complaints:
1. We
have problems with the XW system communicating with the outboard/optional
Automatic Generator Start modules. At one point we were told that the
factory supplied cables were too short and causing "ringing" of the data
signals. We changed out the leads to the prescribed 6' leads and we are
still battling intermittent communications problems with the AGS units.
When the AGS does not communicate, the generator does not start when
needed. The net result is power outages.
2. Schneider created frequent
firmware upgrades. To my mind, this is a sign of half-baked code. The
firmware update process requires an expensive AC powered dongle and an
outboard AC source since the inverters shut down during firmware upgrade.
Upgrading firmware on an XW system was usually a multi-hour affair.
3.
Navigating the SCP is not at all intuitive, in my view.
4. The Power
Distribution Panel is inadequately sized. This is not unique to Schneider,
by any means. For system with more than two inverters we outsourced input
and output AC distribution to outboard QO load centers. The busing of the
AC breakers is via odd, claw-like bus bars. These are a bit awkward to work
with and did not fit every scenario.
5. The XW system had no means to
bypass more than two inverters.
To illustrate these problems, see this
web-page [3].
Due to these problems we decided to concentrate on Outback
and learning how to navigate the short-comings of just one brand. Not
having worked with XW system for a while, I am curious: Have these problems
been resolved?
Thanks in advance.
William Miller
millersolar.com
[4]
805-438-5600
FROM: RE-wrenches
[mailto:re-wrenches-bounces at lists.re-wrenches.org [5]] ON BEHALF OF
Jay
SENT: Sunday, November 18, 2018 11:57 AM
TO: RE-wrenches
SUBJECT: Re:
[RE-wrenches] mate 3s locking
Does Schneider have videos of how to
operate the SCP etc?
Jay
Peltz power.
On Nov 18, 2018, at 7:41
AM, Howie Michaelson wrote:
Drake,
It took me years to try
Trace/Xantrex/Schneider products after swearing off Xantrex in 2004,
becoming an Outback devotee for a decade. I finally soured on Outback a few
years ago after several years of poor customer service and a sense that
Outback was not keeping up in general. I had tried Magnum early on and had
a bad experience with them and the Sunny Island, while a robust machine,
was definitely getting outdated, so I finally decided to give Schneider a
try.
While there are always things I wish could be better in all the
various choices (which is true for the XW as well), I've stuck with
Schneider for a few years now and have been happy with them. I did try the
SWa couple of times, but the small cost savings doesn't feel worth the
lesser capabilities over the XW. And their customer service has been pretty
consistently good.
Howie Michaelson
Sun Catcher
On Sat, Nov 17,
2018, 10:43 AM
Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3]
http://www.millersolar.com/MillerSolar/Portfolio/Commercial/KG/KG_System.html
[4]
http://www.millersolar.com/
[5]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[6]
mailto:Howie.Michaelson at gmail.com
[7]
mailto:drake.chamberlin at redwoodalliance.org
[8]
mailto:re-wrenches at lists.re-wrenches.org
[9]
mailto:william at millersolar.com
[10]
mailto:re-wrenches at lists.re-wrenches.org
[11]
mailto:william at millersolar.com
[12] http://www.millersolar.com/
[13]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[14]
mailto:re-wrenches-bounces at lists.re-wrenches.org
[15]
mailto:re-wrenches at lists.re-wrenches.org
[16]
mailto:RE-wrenches at lists.re-wrenches.org
[17]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[18]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[19]
http://www.re-wrenches.org/etiquette.htm
[20]
http://www.members.re-wrenches.org
[21]
mailto:RE-wrenches at lists.re-wrenches.org
[22]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[23]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[24]
http://www.re-wrenches.org/etiquette.htm
[25]
http://www.members.re-wrenches.org
[26]
mailto:RE-wrenches at lists.re-wrenches.org
[27]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[28]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[29]
http://www.re-wrenches.org/etiquette.htm
[30]
http://www.members.re-wrenches.org
[31]
mailto:RE-wrenches at lists.re-wrenches.org
[32]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[33]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[34]
http://www.re-wrenches.org/etiquette.htm
[35]
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181119/6ea997d0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smiley-wink.gif
Type: image/gif
Size: 350 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181119/6ea997d0/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1777 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181119/6ea997d0/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: combox AGS logs.PNG
Type: image/png
Size: 39501 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20181119/6ea997d0/attachment.png>
More information about the RE-Wrenches
mailing list