[RE-wrenches] Trace SW4024 not selling.
Ray
ray at solarray.com
Mon Nov 12 00:30:40 EST 2018
I'm sure you did this, but did you set menu 9 (Inverter Setup) - Grid
Usage to "SELL" ? Its a whole separate menu heading than "Battery
Selling". That was always a bit of a pain to have to set it in 2
different menu headings.
Ray Walters
Remote Solar
303 505-8760
On 11/11/18 9:53 PM, John Blittersdorf wrote:
> I have a past off-grid customer who has now connected to the grid and
> I installed a transfer switch to allow him to run off-grid or grid
> tied. We have ACIN 1 good and line tie light lit up.. It just
> refuses to sell. Are there any other settings that would impact
> selling beyond the max sell amps and sell voltage?
>
> John Blittersdorf.
>
>