On 8/28/2018 9:59 AM, Rebekah Hren wrote:
> Hi all,
> What you need to do now - to get your voices heard about rapid 
> shutdown requirements-  is to make public comments on the first draft 
> of the 2020 NEC. *_Comments are due AUGUST 30 at midnight!!! _*
>
> Here is the link to a press release 
> <https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review> with 
> links to read the draft and input your comments:
> https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review
>
> The process for changing the NEC is standardized by the NFPA and while 
> it may not be perfect, it's what we've got!
>
> Best,
> Rebekah Hren
>
> On Tue, Aug 28, 2018 at 6:50 AM cwarfel 
> <cwarfel at entech-engineering.com 
> <mailto:cwarfel at entech-engineering.com>> wrote:
>
>     I like your solutions to this. Just sticking to rapid shutdown and
>     not the fire code, I think a lot of the problems with 690.12 could
>     be reduced if the maximum string voltage was 150 or even 250.  It
>     reduces the ampacity on a roof for a given power and I feel that
>     is more of a danger than array voltage that the Firefighters are
>     highly likely to avoid.
>
>     I still cannot get Outback Power to provide a corrected
>     installation manual or a start up procedure on the RSI/ICS
>     equipment. Two plus months and all I get are repeated vague or
>     incorrect information. One expert at OB said that they really
>     didn't deal much with Rapid Shutdown............
>
>     I cannot install any more Outback on roofs at this time.
>
>     I'll see if it is ok to provide a link to an online petition to
>     change 690.12.
>
>
>     Chris
>
>
>
>     On 8/27/2018 2:13 PM, Ray wrote:
>>
>>     HI Chris;
>>
>>     As with all things bureaucratic,  good intentions can go awry
>>     when actually implemented.  Years ago, I was one of the wrenches
>>     pushing for some form of disconnect closer to the power source,
>>     or the PV array.  I had no idea it would come back to bite us
>>     small off grid folks so hard, though.  I'm not quite for
>>     scrapping all of 690.12, but I do think it needs some serious
>>     work. /In or on the building/ needs to be defined more clearly as
>>     'on the roof'. Ground mounts need a clearer exemption. The PV
>>     disconnect needs to be clearly defined and also clearly stated
>>     that the Rapid disconnect system stops there.  The time limit
>>     needs to be bumped up to 90 seconds: no one is going to throw the
>>     switch and be hacking on the roof that fast.  The array voltage
>>     should be 150 vdc, so that lower voltage off grid systems could
>>     be exempt, and I really think 690.12 should only apply to larger
>>     arrays (over 10kW) that have long exposed runs of conduit (over
>>     10 yards) or that cover more than a certain percentage of the
>>     total roof area.  If an array covers one face of the garage it
>>     should be exempt, and if it covers half the total roof, then it
>>     should have Rapid disconnect, for instance.  We need to be
>>     sensible, do the fire fighters have a good spot to cut and vent
>>     the roof without electrical hazards or not?
>>
>>     Its interesting how article 690 has morphed from being almost
>>     entirely oriented towards off grid in 99 and 02, to now off grid
>>     is barely even considered. Just look at the lack of thought when
>>     they wrote the definitions for /DC to DC Converters/.  The solar
>>     industry has been ready and willing to be thrown under the bus at
>>     every turn.  I think its about time we started advocating for our
>>     own self interests like all the other parties involved.  This
>>     also means that us off grid folks need to be properly
>>     represented, and off grid considered with all code changes.  I
>>     think DC coupled PV should have its own section and be separated
>>     from AC coupled PV.  The systems are so different that it doesn't
>>     make sense to throw them into the same section.  The emergence of
>>     article 706 is a step in the right direction.
>>
>>     Ray Walters
>>     Remote Solar
>>     303 505-8760
>>     On 8/23/18 5:31 PM, cwarfel at entech-engineering.com
>>     <mailto:cwarfel at entech-engineering.com> wrote:
>>>
>>>     I think Rapid Shutdown should be scrapped professionally and
>>>     personally.  It was ill conceived and ill written.  Anyone
>>>     willing to join me in a petition to CMP 44 and the like, contact
>>>     me off list.
>>>
>>>     To your question directly, you have a ground mounted system and
>>>     you are not subject to 690.12 unless your conductors are "in or
>>>     on building" which i cannot seem to find what that actually
>>>     means. Exempted are buildings that are isolated only for the PV
>>>     system This is a big win for installers as almost everyone
>>>     installs systems like this....... Right.    They used to have a
>>>     dimension to this, but I guess that gave installers too much
>>>     information. This is a stupid Code addition for roof mounted pv
>>>     systems, disguised as protecting Firefighters, but not doing so
>>>     in reality. The NEC looks politically compromised by consultants
>>>     and manufacturers who too advantage of this fear mongering. No
>>>     other country with a pv industry has historically done this. Why
>>>     are installers not up in arms about this?
>>>
>>>     This is the NEC reference.
>>>
>>>     690.12 Rapid Shutdown of PV Systems on Buildings. PV system
>>>     circuits installed on or in buildings shall include a rapid
>>>     shutdown function to reduce shock hazard for emergency
>>>     responders in accordance with 690.12(A) through (D).
>>>
>>>     If your system is ground mounted, you are outside the
>>>     "altruistic" intent of 690.12 of protecting Firefighters. Put a
>>>     initiation device disconnect switch at the array.  Any
>>>     supporters of RS should chime in with the support of 690.12 and
>>>     add clarity and guidance to those of us who actually install
>>>     systems and have to deal with this baloney.  690.12 has caused
>>>     more problems for multimode systems than any tariffs, which are
>>>     bad enough. I don' think the industry needs any more "safe
>>>     design and installation" assistance from the CMPs involved with
>>>     this issue.
>>>
>>>     Chris Warfel
>>>
>>>
>>>
>>>
>>>
>>>
>>>     On 2018-08-23 00:31, Ray wrote:
>>>
>>>>     Greetings fellow wrenches;
>>>>
>>>>     I know we have beat this many times but I once again have not
>>>>     been able to resolve the contradictory information in 690 in
>>>>     regards to implementing 690.12.  As Rebekah Hren pointed out
>>>>     before, the diagrams shown in Figure 690.1(b) show that the /PV
>>>>     System DC Circuit/ stops at the /PV Disconnect/.  Note 2 says
>>>>     specifically the '/PV Disconnect separates the PV system from
>>>>     all other systems/'.  But then in the definitions in 690.2 on
>>>>     the next page, the new definition of a /P//V System DC Circuit/
>>>>     says that it includes DC to DC converter output circuits. 
>>>>     (which are Solar Edge module level controls, but could be
>>>>     interpreted as a MPPT battery charge Controller?)
>>>>
>>>>     Then 690.12 which only applies to '/PV System circuits in or on
>>>>     buildings/', says we have to control conductors more than 3 ft
>>>>     after penetrating the building.
>>>>
>>>>     So in my case, I'm looking at a ground mount, and installing an
>>>>     external lockable disconnect on the wall before it goes into
>>>>     the building.  This will officially be the PV Disconnect.  In
>>>>     my interpretation, I should not need to do any Rapid Shutdown,
>>>>     because I've essentially prevented the /PV system/ from ever
>>>>     entering the building at all ( based on the 5th diagram and
>>>>     Note 2) However, I could see an AHJ claiming I had to do RS all
>>>>     the way to the output side of the charge controller.
>>>>
>>>>     If this were true, could I simply apply RS equipment from the
>>>>     PV disconnect to the output of the charge controller, or am I
>>>>     back to module level shutdown for my ground mounted array, or
>>>>     could I build a tiny building that just housed the PV
>>>>     Disconnect and take the exemption for '/buildings with the sole
>>>>     purpose of housing PV system equipment/'?
>>>>
>>>>     Essentially the definitions in 690.2 are too broad, and are at
>>>>     odds with the Figure and Notes of 690.1.  They really didn't
>>>>     fix this in the 2017 code for us lowly off gridders. Charge
>>>>     controllers are covered by article 706.23___/Charge Control/_,
>>>>     and NOT by 690.12 at all. IMHO, the charge controller needs to
>>>>     be clearly defined and differentiated from DC to DC converters
>>>>     like Solar Edge's module level DC equipment.
>>>>
>>>>     I just want to go back to doing solar designs and
>>>>     installations, and quit acting like an attorney parsing every
>>>>     word of this confusing code language.
>>>>
>>>>     -- 
>>>>     Ray Walters
>>>>     Remote Solar
>>>>     303 505-8760
>>>>
>>>>     _______________________________________________
>>>>     List sponsored by Redwood Alliance
>>>>
>>>>     List Address: RE-wrenches at lists.re-wrenches.org
>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>>     Change listserver email address & settings:
>>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>>     List-Archive:
>>>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>
>>>>     List rules & etiquette:
>>>>     www.re-wrenches.org/etiquette.htm
>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>
>>>>     Check out or update participant bios:
>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>
>>>
>>>
>>>     _______________________________________________
>>>     List sponsored by Redwood Alliance
>>>
>>>     List Address:RE-wrenches at lists.re-wrenches.org
>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>     Change listserver email address & settings:
>>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>     List rules & etiquette:
>>>     www.re-wrenches.org/etiquette.htm
>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>     Check out or update participant bios:
>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>
>>
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address:RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>     -- 
>
>              Christopher Warfel, PE
>            ENTECH Engineering, Inc.
>     PO Box 871, Block Island, RI 02807
>                    (401)466-8978
>
>     EEI logo <http://entech-engineering.com>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> -- 
> Tel: 336.266.8800
> NABCEP Certified Solar PV Installation Professional™ 091209-85
> NC Licensed Electrical Contractor
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 

          Christopher Warfel, PE
        ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                (401)466-8978

EEI logo <http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180828/248e5e37/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180828/248e5e37/attachment.jpg>


More information about the RE-Wrenches mailing list