[RE-wrenches] SOC and LFP batteries and TriMetric
Sindelar Solar
Allan at sindelarsolar.com
Tue Aug 21 15:26:18 EDT 2018
Yes, I just did. Ralph retired last year and I spoke with the new owner.
In short, little change - use 2% of capacity for amp threshold and set
CEF to 98% from default 94%. I was also told to stick with the default
14.1V voltage threshold, but that equates to 56.4V for a 48V system,
which is above the normal range of these batteries, so I'm reluctant to
take that advice.
I'm working with Kyle Bolger of Blue Planet on this first installation,
and will post to the list what I learn that will benefit others.
Thank you, Allan
On 8/21/2018 11:29 AM, Howie Michaelson wrote:
> Allan, have you talked directly with Bogart?
> Howie
>
> On Tue, Aug 21, 2018 at 12:56 PM Sindelar Solar
> <Allan at sindelarsolar.com <mailto:Allan at sindelarsolar.com>> wrote:
>
> Wrenches,
> I would like to broaden this topic a bit, please: we're currently
> installing our first Blue Ion LFP set (48kWh). I work almost
> exclusively with existing off grid systems, often older systems
> most of which have TriMetric monitors, either the TM2020 or newer
> TM2030. Has anyone successfully reprogrammed a TriMet to
> accurately register SOC and other data with LFP batteries? If so
> can you provide some guidance as to program settings?
> Thank you,
> Allan
>
--
*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180821/140de869/attachment.htm>
More information about the RE-Wrenches
mailing list