[RE-wrenches] DC-DC converter for SQFlex

MDElectricSolar mdelectricsolar at gmail.com
Tue Aug 21 14:24:00 EDT 2018


Is there an inverter, you could power it with 120 or 240V AC?

On Tue, Aug 21, 2018 at 11:17 AM Gary Higbee <gary at windstreamsolar.com>
wrote:

> Hi Wrenches,
>
> I’m assisting a customer and well person in replacing a failed Lorentz
> ETApump (after 15 years of intermittent use). We’re looking for a quality
> DC-DC converter to power a not-yet- ordered Grundfos SQFlex 6 SQF-3 from a
> 24 V Surrette battery bank (wish it was 48!). The pump draws a max of 8.4A
> and the curves say we’ll need about 600 watts so I figure we’d want at
> least 70 volts out. Ideal would be a higher DC output, say 200V (save a
> couple hundred feet of larger copper, greater efficiency) and at least 3A
> (see questions).
>
> The primary power source will be 240V AC but my customer wants a fallback
> for battery operation. We plan to use the Grundfos IO 101 SQFlex switch
> box, which will switch to DC if the AC fails. Also the CU 200 SQFlex
> control unit, so we can accommodate the existing float switch up the hill,
> etc.
>
> The Grundfos tech person I spoke with today said the DC system should be
> able to supply 8.4A, regardless of the DC voltage.The pump curve says we
> need 600W for maximum performance at the lift we’ve got. It seems to me
> that if we’ve got 200V and need 600W we’d be drawing 3A. Yet if the
> Grundfos factory line is there should be 8.4A available that’s 1680W. The
> tech guy said he didn’t have specific information why we’d need 8.4A
> regardless of pump input voltage.
>
> The Grundfos Product Guide says:
>
> *Max. ratings are as follows:*
> *• Maximum power input (P1) of 1400 W*
> *• maximum current of 8.4 A*
> *• maximum speed of 3600 rpm *(think I read somewhere it’s 3000 rpm for
> this helical rotor model)
>
> *The pump delivers its maximum performance when **one of the above
> parameters is reached.*
>
> Two questions:
>
> 1) Do any of you have experience running the SQFlex on DC, and what to
> make of the 8.4A at any input voltage factory recommendation? Maybe basic
> amps/volts/power calculations aren’t applicable given the pump electronics?
>
> 2) Are you aware of any DC-DC converters that will get us from a nominal
> 24V battery bank to 200V, or somewhere between 70 and 200V, with an
> appropriate current limiting amp rating to get us at least 600W (depending
> on thoughts regarding the above question)?
>
>
> Thank you,
>
> Gary
>
> Gary Higbee
> Windstream Solar
> Oregon License 17LRT
> Renewable Energy Consulting
> gary at windstreamsolar.com
> 541-954-3881
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-884-1862
Cell: 707-684-0064
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180821/05a68060/attachment.htm>


More information about the RE-Wrenches mailing list