[RE-wrenches] Tapping Parallel Conductors
Garrison
garrison.rie at gmail.com
Tue Aug 21 11:09:02 EDT 2018
Hi Wrenches,
When making a supply side connection on parallel sets of conductors is it required to tap all conductors on each phase?
I have a set of plans with an 800A interconnection on a 1200A service. Service has three parallel sets of 500MCM. Plans call for tapping just two conductors on each set of three. Plans are stamped by an EE. I had been working under the assumption that if tapping parallel sets all conductors must be tapped.
Any issues with not tapping all sets?
Thanks,
Garrison Riegel
Rethink Electric
630-998-3629