[RE-wrenches] battery temp sensors for older Trace/Xantrex inverters

Chris Schaefer chris at solarandwindfx.com
Mon Aug 6 15:17:01 EDT 2018


To All,

Since I have two Xantrex/Trace SW5548's that run my shop/office and home
(offgrid) I decided to take some time early this morning to  install a
MidNite and Outback BTS into one of the inverters to see first hand what
the results would be. Below is the results with the actual voltage @ 49.2.
The compensated voltage shown on the Trace screen was;
MidNite; 56.2
Outback: 55.2
While the original Trace bts returned a compensated voltage of 49.8. I did
allow for a 30 minute adjustment to the environment before recording values.
Thus I walked away proving to myself that you can't (as many of you have
pointed out) cross use either MidNite or Outback bts on the SW.
Ray thanks for the offer of the BTS but since Dave has graciously provided
us with the Xantrex/Schneider p/n 130-0004-01-01 I'm going to see if I
can't locate a couple through the normal vendors.

Thanks everyone,
Christopher



On Mon, Aug 6, 2018 at 11:09 AM, Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:

> From Schneider
>
> *Resolution:*
> Product Family Xantrex Part Number
> Conext XW, Conext SW, TR, Truecharge2*, XC chargers*, FSW2000* 808-0232-01
> Trace SW, CR*, DR, RV*, C series 130-0004-01-01
> Trucharge20+/40+*, Prosine 3.0* 808-0231
> RS/MS*, RV/GS series*, FSW3000*, FSW2012*, FSW3012*, Prosine 2.0* 809-0946
> FDM 458* / FDM Marine* 76-0022-00
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
>
>
> On Mon, 6 Aug 2018 14:40:21 +0000, Lones Tuss <ltuss at outbackpower.com>
> wrote:
>
> Hello All
>
> The Trace Battery Temp sensor has a 100 k negative coefficient.
>
> The Outback Battery temp sensor has a 10 K negative coefficient.
>
> The Outback temp senor will not work with Trace equipment.
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Chris Schaefer
> *Sent:* Saturday, August 4, 2018 2:05 PM
> *To:* re-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* [RE-wrenches] battery temp sensors for older Trace/Xantrex
> inverters
>
>
>
> Good Day All,
>
>
>
> Running into a lot of missing or chewed up battery temp sensors for the
> older Trace inverters. I'm looking for potential replacements. Anyone had
> any luck using another vendor or do you have a direct replacement source
> for these?
>
>
>
> Thanks,
>
> Christopher-
>
> Chris Schaefer's
> <http://www.solarandwindfx.com>
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870  *
> *5115 South Hill Road ~ Canandaigua New York 14424 www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: **chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
>
> --
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Chris Schaefer’s
<http:www.solarandwindfx.com>

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
<chris at solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180806/0ed834d3/attachment.htm>


More information about the RE-Wrenches mailing list