[RE-wrenches] battery temp sensors for older Trace/Xantrex inverters

Dave Angelini Offgrid Solar offgridsolar at sti.net
Mon Aug 6 11:04:43 EDT 2018



I have also seen this problem when tweaking XW and CSW's


ENVIRONMENT
There is a "Battery Temperature Coefficient" value that is
set to -84 and seems can't be changed. My battery bank's datasheet calls
for -108 mV/C. When this value is changed, and saved, the message "The
value could not be changed" is displayed.

CAUSE
Customer is using the
wrong Battery Type on the XW+'s Charger Settings

RESOLUTION
The Battery
Bank Type should be set for custom (in the custom battery settings), then
the Battery Temperature Coefficient will be adjustable.  
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridsolar at sti.net
[2]
text 209 813 0060

On Mon, 6 Aug 2018 14:40:21 +0000, Lones Tuss 
wrote:      

Hello All 

The Trace Battery Temp sensor has a 100 k
negative coefficient. 

The Outback Battery temp sensor has a 10 K negative
coefficient. 

The Outback temp senor will not work with Trace equipment.


FROM: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] ON
BEHALF OF Chris Schaefer
 SENT: Saturday, August 4, 2018 2:05 PM
 TO:
re-wrenches 
 SUBJECT: [RE-wrenches] battery temp sensors for older
Trace/Xantrex inverters 

Good Day All,  

Running into a lot of missing or
chewed up battery temp sensors for the older Trace inverters. I'm looking
for potential replacements. Anyone had any luck using another vendor or do
you have a direct replacement source for these?   

Thanks,  


Christopher-        

Chris Schaefer's
  [3]
 Tel/Fax 585-229-2083 or
Cell 585-748-1870 
 5115 South Hill Road ~ Canandaigua New York 14424

www.solarandwindfx.com [4] ~ E-mail: _chris at solarandwindfx.com [5]_ 

__


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."           -- 




Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridsolar at sti.net
[3] http://www.solarandwindfx.com
[4]
http://www.solarandwindfx.com
[5] mailto:chris at solarandwindfx.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180806/b9e37bc8/attachment.htm>


More information about the RE-Wrenches mailing list