Article 110.26 covering clearances in front of electrical equipment
applies. I worked on a couple like that, and I didn't like it. Very
hard to move the batteries, and Combined with H2S, you are in what OSHA
considers a confined hazardous space.
Another way to use that crawl space is to build a trap door access from
the floor above. This can work really nicely, and put the batteries
right under the inverter without violating article 110.26. I think I
saw a system that either Allan Sindelar or Windy Dankoff did like that.
I've tried it a few times, and everyone (customers and inspectors) was
happy. Here's a pic of some HUPs in a floor vault just below the inverter:
Ray Walters
Remote Solar
303 505-8760
On 7/30/18 8:37 AM, Dana wrote:
>
> Safe working clearance is 6’-8”.
>
> I have been confronted with this issue in the past taking over other’s
> systems care. This is a head banger & a major safety issue if
> something goes bad. If the batteries are 18-20” tall that only leaves
> anther 28-30” between bottom side of the floor joist & the top of the
> battery. Your face is way too close to a battery esp. if there is an
> issue to address.
>
> The installation is bent over back-heavy move situation. I am assuming
> you have a dirt or gravel floor to move across?
>
> It seems like a good use of space up front but the reality of the
> install plagues you down the road.
>
> If it is WLA batteries it is the worst of situations.
>
> Even if this is not inspected, please avoid this situation.
>
> ----------------------------------------------------------------------------
>
> Dana Orzel Great Solar Works, Inc.
>
> *C - 208.721.7003 dana at solarwork.com*
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136 www.solarwork.biz <http://www.solarwork.biz>
>
> _"Responsible Technologies for Responsible People since 1988" ___
>
> *P*Please consider the environment before printing this email.
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Jerry Caldwell
> *Sent:* Saturday, July 28, 2018 6:10 PM
> *To:* re-wrenches at lists.re-wrenches.org
> *Subject:* [RE-wrenches] Batteries in 4' tall crawl space
>
> Wrenches,
>
> I have a customer who wants to have batteries installed in a 4' tall
> crawl space / short basement. Are there any accessibility code issues
> with installing batteries in a crawl space? Does the NEC address this?
>
> Thanks,
> Jerry Caldwell
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180730/314f7197/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: lkgdjlojbdoibepi.jpg
Type: image/jpeg
Size: 62652 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180730/314f7197/attachment.jpg>
More information about the RE-Wrenches
mailing list