Thank you all for the ideas and suggestions. This person in particular had
#4 wire for the battery connections,
so they are all getting replaced with anyway. So it seems like rewiring to
a busbar with fuses will be the way to
go. And although not ideal to have so many strings, this will be more cost
effective than just getting a whole new
battery bank right off the bat when they have 10 batteries that have
essentially never been used.
Cheers,
Dave
*--*
*Dave Tedeyan*
*Senior Engineer*
*Taitem Engineering, PC*
10 Verizon Lane, Lansing, NY 14882
Voice: (607) 930-3481 x6
www.taitem.com
On Mon, Jul 23, 2018 at 8:50 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:
> Hi Christopher,
>
>
>
> I buy my copper buss material from McMaster Carr in appropriate dimensions
> for the current I am expecting.
>
> I then cut it to the lengths I need, drill for appropriate size fasteners
> and use 2 layers of heat-shrink tubing to protect the exposed bar.
>
>
>
> Hope this helps.
>
> -Glenn
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Chris Schaefer
> *Sent:* Monday, July 23, 2018 2:28 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] 5 battery strings
>
>
>
> What source are you all using for buss bars for these multiple battery
> string set ups?
>
>
>
> Christopher
>
>
>
> On Mon, Jul 23, 2018 at 2:16 PM, <tom at wagonmaker.com> wrote:
>
> Separate out the individual series strings and run each string to a buss
> bar setup. Remember it isn't just resistance differences between batteries
> but resistance difference between cells as well. In a setup like the
> existing one the resistance differences can really add up and if one
> battery fails the entire system will be offline. Running each string to a
> positive and negative common buss bar means you can remove individual
> strings without disrupting the entire storage and the system can continue
> operating. Also, it means the only resistance issues of substance are
> within individual series pairs not the entire interconnected bank.
>
> I ran 10 series pairs of 12v AGM batteries, each pair to a common buss and
> it was the longest lasting, most stable battery bank I had. That was years
> ago and now it would require fusing each string but for longevity and
> stability it is the best bet.
>
> Tom
>
> On 2018-07-23 03:56, Dave Tedeyan wrote:
>
> Since we are on the topic of bad battery practices...
>
> I may be fixing up a system that was both designed and installed very
> poorly.
> They have a 24V Outback VFXR inverter, and ten 12V AGM batteries wired
> into
> 5 parallel strings. I know that is a bad idea, but since they already
> have the
> equipment, are there any safety issues by re-using this equipment? It
> is for a
> grid tie battery backup system that will remain in float most of the
> time. I assume
> that the batteries will not last particularly long, but is there any
> harm in using them
> and then just getting new batteries once they fail?
>
> Stringing is shown in the attached picture.
> Cheers,
> Dave
>
> --
>
> Dave Tedeyan
>
> SENIOR ENGINEER
>
> TAITEM ENGINEERING, PC
> 10 Verizon Lane, Lansing, NY 14882
> Voice: (607) 930-3481 x6
> www.taitem.com [1]
>
> Links:
> ------
> [1] http://www.taitem.com/
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
>
> --
>
> Chris Schaefer’s
> <http://www.solarandwindfx.com>
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: **chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180724/22a4a708/attachment.htm>
More information about the RE-Wrenches
mailing list