[RE-wrenches] Electrolyte Dilution vs Voltage
John Blittersdorf
john.blittersdorf at gmail.com
Wed Jul 18 21:24:20 EDT 2018
Mac,
I was about to ditto Ray with his more common than I would like scenario
of battery death when I saw your mention of the 2nd string not connected.
It is always nice to see
a solution that is simple and should have been considered, but wasn't. The
assumption with battery issues usually is that they are actually hooked
up! I often thought that it would be worth the money to supply a cheap
AC/DC clamp meter with every installation so that a phone consultation
could quickly determine if the strings were unbalanced and what might be
the reason. Bad cells and bad connection will usually show up in a
current check and then a quick voltage check of each battery with a load on
the system will show the culprit if a bad cell and corrosion present might
find the bad connection. I use Interstate L16's most of the time and find
that the life is typically 6 years. I used to call them a 7 to 10 year
battery but kept racheting back the claim until I now call them a 5 to 7
year battery with more if properly maintained. I have seen 10 years but it
is rare.
John Blittersdorf
Off grid specialist
Rob Stubbins Electrical and Solar.
On Wed, Jul 18, 2018 at 1:28 PM, Mac Lewis <maclewis1 at gmail.com> wrote:
> Hi guys,
>
> I appreciate the answers and comments.
>
> However, I did find out from her that she had forgot to connect one of the
> strings back in. So maybe we are OK.
>
> Thanks again
>
> On Wed, Jul 18, 2018 at 11:16 AM Ray <ray at solarray.com> wrote:
>
>> Interstate is not a long life battery. 5 years is probably getting near
>> the end. As they age, they start using more water which leads to running
>> them dry, which leads to killing them even quicker. The end of service for
>> L16s is usually not pretty. I'd be checking for dead cells, in addition to
>> Steve Higgins's recommendations. Whether she can recover them or not, its
>> time to at least start shopping for new batteries. As this continues,
>> they'll use more and more water, make more acid mess, and in general not
>> work as well from here on out. Then, cells will start dying left and
>> right, and it will get really miserable. Basically it comes down to how
>> long she is willing to suffer.
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>
>> On 7/18/18 9:38 AM, Mac Lewis wrote:
>>
>> Hello Wrenches,
>>
>> I have a homeowner client that takes pretty good care of her batteries.
>> She has a 5 year old set of Interstate L16s (2 strings of 8). However, she
>> recently didn't water them for longer than normal and they gulped up more
>> distilled water than usual (4 gallons). She was unsure if any of the
>> plates were exposed. She has reported that since she added the water the
>> battery bank has lost about 1.5-2V (48V bank) of her bank voltage in the
>> morning. She reported ~49.5V in the morning before she added the water and
>> now she is below 48V.
>>
>> I have advised a good strong equalize charge to destratify the
>> electrolyte.
>>
>> Will diluting the electrolyte make the voltage sag like that? Is there
>> any other advice you might give her until I can get up there?
>>
>> Thanks
>>
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> * "Yo solo sé que no sé nada." -Sócrates *
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180718/e11e0861/attachment.htm>
More information about the RE-Wrenches
mailing list