[RE-wrenches] Solar set backs
Daniel Young
dyoung at dovetailsolar.com
Tue Jul 10 17:25:01 EDT 2018
Hey Gary,
Ohio Fire Code does cover this. It’s a matter of if the Fire marshal in you project area wants to waive or alter the requirements.
http://codes.ohio.gov/oac/1301:7-7-06v1
Specifically 605.11.1.2 is for residential buildings. There is some conflict in terms of Hip roofs in the code there. 605.11.1.2.2 states a single 3ft path on one edge or another for a hip roof, but 605.11.1.2.4 states that an 18 space is allowed when modules are mounted on two adjacent roof planes with a hip roof.
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of gary easton
Sent: Monday, July 09, 2018 3:39 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Solar set backs
Hello Wrenches,
What are you all seeing required as setbacks post 2017? I am having inspectors vary between wanting a 3' lane at the bottom and sides to allowing the array down to the gutter, and from requiring between 18" and 3' at the ridge.
--
Gary Easton