[RE-wrenches] Xfmr's job?
Lones Tuss
ltuss at outbackpower.com
Sun Jul 8 07:47:51 EDT 2018
Hello All
The VFX/FX inverters does make use of the X240 transformer.
The transformer itself could act as a step up, a step down, or a load balancing transformer.
Neither the FXR or the Radian inverters require the transformer as a load balancing transformer.
The transformer can still be used in its step up or step down configurations.
The FXRA does not use the transformer for load balancing therefore each inverter must be sized to handle the loads
and any associated surges as required by the ac loads on that leg.
What was lost was the ability of the inverter systems to "borrow" from the lessor used ac leg.
What was gained.
The FXRA can sell back with up to 10 inverters compared to two of the GVFX .
The FXRA can have up to 9 inverters in a 3 phase system compared to 3 with the VFX.
The FXRA has seven modes of operation allowing on grid or off grid operation.
SA capabilities are also available.
The question "How much wattage could be supplied by the Radian on a single AC leg" was also asked.
I put 6000 watts on L1 leaving no loads connected to the L2 phase.
I will add this is not recommended practice.
The loads should be balanced at the ac panel as closely as possible.
But real life conditions are not always ideal.
I hope this helps to clarify.
Take Care All
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Angelini Offgrid Solar
Sent: Wednesday, May 30, 2018 7:53 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Xfmr's job?
The 8kw radian still has to have balance! You can't expect it to supply 8kw @ 120vac. It can supply 8kw @ 240 vac.
> Does each of the 4 kW 240 volt inverters have a maximum on the
> 120-volt power it can supply? for example, can it supply 70% of the 4
> kW on 120 -volts?
> This example would leave 5.6 kW of 120-volt?
>
> On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01
> <jerrysgarage01 at gmail.com>
> wrote:
>
>> The Radian has 2, 4k, 240 volt inverters, so its different but the
>> way the computer works it makes the same from the load side of things
>> Jerry
>>
>>
>>
>> Sent from my Verizon, Samsung Galaxy smartphone
>>
>>
>> -------- Original message --------
>> From: frenergy <frenergy at psln.com>
>> Date: 5/29/18 5:51 PM (GMT-10:00)
>> To: re-wrenches at lists.re-wrenches.org
>> Subject: [RE-wrenches] Xfmr's job?
>>
>> Hey folks,
>>
>> Outback FP2 with Xfrmr shifts power to "other" leg if
>> that leg needs more than the one FX can provide, right? Say, you
>> need 5.5 KW on leg 1, the Xfrmr pulls some power from the leg 2
>> (inverter) to support that 5.5KW load on leg 1.
>>
>> My question (assuming above is accurate) is does the 8048 Radian do
>> the same?
>>
>> Thanks,
>>
>> Bill
>>
>> Feather River Solar Electric
>> Bill Battagin, Owner
>> 4291 Nelson St.
>> Taylorsville, CA 95983
>> 530.284.7849
>> CA Lic 874049
>> www.frenergy.net
>>
>>
>> ---
>> This email has been checked for viruses by Avast antivirus software.
>> https://www.avast.com/antivirus
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
> .html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list