[RE-wrenches] grounding on metal roofs

Jason Szumlanski jason at floridasolardesigngroup.com
Tue Jul 3 15:21:37 EDT 2018


Local AHJs here have sometimes required/accepted a single listed lug on a
single pan. How you seal that effectively and permanently is a mystery to
me, but what's more of a mystery is the sensibility of the conclusions they
reach. Unless every pan, cap, and flashing within reach of an energized
conductor is bonded using a listed lug, how would this work effectively?
S-5 clamps or other attachment fasteners are probably just as effective at
creating a bonding path as and roof pan fastener, but definitely can't be
relied upon from a code/listing perspective. Maybe we need to encourage
metal roofing manufacturers to get 2703 listing (haha - right).

Side note: I don't see AHJ's worrying about overhead service conductors
potentially energizing a metal roof. I've seen some pretty shaky rusted out
weatherhead pipes and downed poles in storms with overhead conductors
laying on roofs.


Jason Szumlanski





On Mon, Jun 18, 2018 at 3:32 PM Glenn Burt <glenn.burt at glbcc.com> wrote:

> NEC 250.4(A)4 Also states that normally non-current-carrying electrically
> conductive materials that are likely to become energized shall be connected
> together and to the electrical supply source in a manner that establishes
> an effective ground-fault current path.
>
>
>
> So the logic goes if an array develops a ground fault, and the faulted
> conductor contacts a metal roof surface, there is a possibility that the
> roof may become energized. So for many reasons, bond the roof to ground.
>
>
>
> -Glenn
>
> Renewable Energy Engineer – Cadmus
>
> Principal Engineer – Power Guru
>
> Principal – glb, Consulting Company
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *bruce at willpowerelect.com
> *Sent:* Monday, June 18, 2018 1:42 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>; AE Solar <
> autonomousenergies at gmail.com>
> *Subject:* Re: [RE-wrenches] grounding on metal roofs
>
>
>
> NEC 690.47 (A) requires the array to be grounded, not necessarily the
> roof. If you have bonded the rails and modules and your grounding conductor
> goes back to the service you should be good. 690.47 (B) allows installation
> of an auxiliary grounding electrode (ground rod or building steel). Not a
> bad idea in lightning prone areas. ;) Local AHJ may have different opinions.
>
>
>
> Bruce Fiero-RMI
>
>
>
>
>
> *"Energizing the Rogue Valley"*
>
>
>
> *4115 S Pacific Hwy*
>
> *Medford, OR 97501*
>
>
>
> *P:* 541.535.3965
> *F:* 541.512.0061
> *E:* bruce at willpowerelect.com
> *W:* Willpower Electric, LLC <http://www.willpower-electric.com>
>
>
>
> *CCB **191852*
> *Oregon Electrical Contractor **C681*
> *NABCEP Certified Solar (PV) Installer **031409-38*
>
> *DUNS* *191470363*
>
> *Energy Trust of Oregon Trade Ally **Solar (PV) Installation & Energy
> Efficient Commercial Lighting Programs  *
>
>
>
>
> ***This email may contain information that is privileged, confidential, or
> otherwise exempt from disclosure under applicable law. If you are not the
> addressee, or if it appears that you have received this email in error,
> please advise me immediately by reply email, keep the contents
> confidential, and immediately delete the message and any attachments from
> your system. *
>
>
>
>
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] grounding on metal roofs
> From: "glenn.burt at glbcc.com" <glenn.burt at glbcc.com>
> Date: Sun, June 17, 2018 6:17 pm
> To: AE Solar <autonomousenergies at gmail.com>
> Cc: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>
> Depends on the seam profile. Same device may be used in many cases. We
> have Also drilled and used the standard direct burial lugs on the underside
> of the pans, at the wave when they hang over enough to get working space.
> Then a horizontal run of copper wire to connect.
>
>
>
> Don't be lulled into thinking that S-5 clamps are listed for grounding
> roof pans - they are not. They are only listed for module bonding to ground.
>
>
>
> Sent from my 'smart' phone so please excuse spelling and typos.
>
>
>
> ------ Original message------
>
> *From: *AE Solar
>
> *Date: *Sun, Jun 17, 2018 8:46 PM
>
> *To: glenn.burt at glbcc.com <glenn.burt at glbcc.com>;*
>
> *Cc: RE-wrenches;*
>
> *Subject:Re: [RE-wrenches] grounding on metal roofs*
>
>
>
> *thanks glenn. and what about commercial? anyone have code references
> regarding grounding when doing solar on metal roofs? i thought a few years
> back there was a conversation on this but i can't seem to find it.*
>
>
>
>
> *Adam KatzmanAutonomous EnergiesPO Box 1245*
>
>
>
> *Kingston, NY 12402www.autonomousenergies.com
> <http://www.autonomousenergies.com>(518) 567-1468 <(518)%20567-1468>*
>
>
>
> *On Sun, Jun 17, 2018 at 1:46 PM, glenn.burt at glbcc.com
> <glenn.burt at glbcc.com> <glenn.burt at glbcc.com <glenn.burt at glbcc.com>> wrote:*
>
> *We use the Ilsco SGB-4 ground lug on every pan under the array for
> residential systems.*
>
>
>
> *-Glenn*
>
>
>
> *Sent from my Verizon LG Smartphone*
>
>
>
> *------ Original message------*
>
> *From: AE Solar*
>
> *Date: Sun, Jun 17, 2018 12:29 PM*
>
> *To: RE-wrenches;*
>
> *Cc: *
>
> *Subject:[RE-wrenches] grounding on metal roofs*
>
>
>
> *wrenchers,*
>
> *what methods are you all using for grounding on metal roofs? thanks*
>
> *adam*
>
>
>
>
> *Adam KatzmanAutonomous EnergiesPO Box 1245*
>
>
>
> *Kingston, NY 12402www.autonomousenergies.com
> <http://www.autonomousenergies.com>(518) 567-1468 <(518)%20567-1468>*
>
>
> *------------------------------*
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> *_______________________________________________List sponsored by Redwood
> AllianceList Address: RE-wrenches at lists.re-wrenches.org
> <RE-wrenches at lists.re-wrenches.org>Change listserver email address &
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>List
> rules & etiquette:www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>Check out or update participant
> bios:www.members.re-wrenches.org <http://www.members.re-wrenches.org>*
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180703/3e54412e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4536 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180703/3e54412e/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4536 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180703/3e54412e/attachment-0001.jpg>


More information about the RE-Wrenches mailing list