The first thought I have is the inverters have a maximum input current
rating if you parallel then
you need overcurrent protective device downstream from the paralleling
disconnect.  Also PV systems 690.13
must disconnect all conductors from all sources of power.
I agree your solution appears to be correct.  multiple inverters on a
single disconnect happen with microinverters.

On Thu, Jun 21, 2018 at 9:26 AM Advanced Energy Solutions <tech at aessolar.com>
wrote:

> I ran 2 inverters through the same 3 blade (using 2 blades with one leg of
> each inverter going though) disconnect but the utility engineer wants me to
> have a disconnect for each inverter.
>
> I can't find the code that says that is allowed
>
> --
> I invite you to visit our showroom at 1804 Supply Road Carterville IL.
>
> #GetEnergized w/Renewable Energy #GoSolar, PEACE>
> Aur J Beck,
>
> PV Installation Professional™ certification #032611-24
> PV Technical Sales Professional™ PVTS032412-6
> chief tech of Energy Network (Green Geek Squad*™ *)
> Advanced Energy Solutions Group, Inc
> (618) 893-1717 | (800) 229-0453  | www.AESsolar.com
> <http://www.aessolar.com/> | tech at AESsolar.com <tech at aessolar.com>
>
> We Empower YOU to Get Energized!
>
> Why choose us:
> Installing since 1999
>
> PV Installation Professional™ certification #032611-24
> PV Technical Sales Professional™ PVTS032412-6
> We only do solar so we are not doing this part time
> Our chief tech has lived off grid for 18 years
> We have designed and worked on tiny off grid systems all the way up to
> 100kW systems
> We have a strong focus on education so we try to set up systems to be
> showcased
> We design and install systems to last the full 25 year warranty of the
> modules
>
> Be an Energy Patriot
>
> Living on Earth is Expensive, but it does include a FREE trip around the
> Sun!
>
> Oil Addicts Anonymous International (a real 12 step program)
> www.IamanOilAddict.org <http://www.iamanoiladdict.org/>
>
> This communication is the property of Advanced Energy Solutions Group, Inc
> and is intended only for use by the recipient identified. If you have
> received this communication in error, please immediately notify the sender
> and delete the original communication. Any use of this message without the
> Advanced Energy Solutions Group, Inc's consent is prohibited.
> ü Please consider the environment before printing this email.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180621/9111c943/attachment.htm>


More information about the RE-Wrenches mailing list