[RE-wrenches] grounding on metal roofs
glenn.burt at glbcc.com
glenn.burt at glbcc.com
Sun Jun 17 21:17:02 EDT 2018
Depends on the seam profile. Same device may be used in many cases. We have Also drilled and used the standard direct burial lugs on the underside of the pans, at the wave when they hang over enough to get working space. Then a horizontal run of copper wire to connect.
Don't be lulled into thinking that S-5 clamps are listed for grounding roof pans - they are not. They are only listed for module bonding to ground.
Sent from my 'smart' phone so please excuse spelling and typos.
------ Original message------From: AE SolarDate: Sun, Jun 17, 2018 8:46 PMTo: glenn.burt at glbcc.com;Cc: RE-wrenches;Subject:Re: [RE-wrenches] grounding on metal roofs
thanks glenn. and what about commercial? anyone have code references regarding grounding when doing solar on metal roofs? i thought a few years back there was a conversation on this but i can't seem to find it.
Adam Katzman
Autonomous Energies
PO Box 1245Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468
On Sun, Jun 17, 2018 at 1:46 PM, glenn.burt at glbcc.com <glenn.burt at glbcc.com> wrote:
We use the Ilsco SGB-4 ground lug on every pan under the array for residential systems.
-Glenn
Sent from my Verizon LG Smartphone
------ Original message------From: AE SolarDate: Sun, Jun 17, 2018 12:29 PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] grounding on metal roofs
wrenchers,what methods are you all using for grounding on metal roofs? thanksadam
Adam Katzman
Autonomous Energies
PO Box 1245Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180617/b6ad2736/attachment.htm>
More information about the RE-Wrenches
mailing list