[RE-wrenches] Large Off Grid Inverter?
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Thu Apr 26 19:58:19 EDT 2018
I know Schneider would love to sell you their cluster of 15 XW6848+ for a
max of 102KW and probably well over 300KW of surge.
Here is a link to their commercial offgrid. I do own their stock and other
companies also :) Their commercial engineers are pretty smart about this.
https://solar.schneider-electric.com/solution/commercial-off-grid-solar-2/
This does sound like a challenge and keep us informed on what you do
please! Good Luck! --Dave
> Hello Ray,
>
> I have a couple 60/100 kW SMA Sunny Island systems out there, systems with
> 100 kW generators, 400 kWh battery banks and generally token renewable
> inputs. I feel with this configuration we close maxing out what can be
> done with 48VDC.
>
> Getting into the MW scale scares me to be honest. I think that will be
> well beyond what can be handled at 48VDC and is well beyond capacity of
> the SMA systems. Really need to look into higher DC voltages to handle
> this kind of current.
>
> If this was my client I would first look to the loads and see if there are
> any alternatives to the 250 HP motor. I have learned there are often
> massive levels of engineering overkill in the industrial world. What is
> the duty cycle of that motor, what does it do, etc? Would they be better
> to go directly diesel for that?
>
> In terms of system designs I'd investigate a direct diesel/PV interface
> skipping battery storage. Perhaps a group of 250 kW synchronized
> generators that can ramp up/down based on demand. Perhaps similar tech to
> what Tesla is doing in Australia.
>
> Kevin
>
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of Ray
> Sent: April-25-18 12:37 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: [RE-wrenches] Large Off Grid Inverter?
>
> Greetings Fellow Wrenches;
>
> We are consulting on a power system for a large off grid facility that is
> currently operating on a 1500 kW gen set. The loads are enormous for
> normal off grid: in the neighborhood of 600 amps continuous at 480 v 3
> phase. Surges are close to 2000 amps, but we are working on control
> programming to bring that number down substantially. That is due
> primarily to a 250 Hp motor start. (that's not a typo!). EPA and local
> regulations are dictating that the current generator be retired in the
> near future. Grid power is a possibility, but we need to offer a viable
> off grid option as well.
>
> My question to the group: does anyone have real off grid experience with
> large format battery based inverters?  I've heard of some micro-grid
> systems running in Haiti on Princeton Power inverters, and Dynapower has a
> 250 kW inverter that has a "grid forming" mode. As we all know, it is
> easier to make claims in spec sheets than to deliver hard motor starting
> power in a remote location. We need proven products, with a track record
> of reliability.
>
> We are considering SMA type systems that use AC coupled PV to offset fuel
> consumption of a generator, but those seem dependent on the generator to
> maintain the stability of the micro grid during hard starting loads.
> Ideally we would want to reduce the generator run time to under 200 hrs/
> yr and reduce its size to 500 kW. We have excellent solar resources year
> round, and the possibility of limiting operations during cloudy weather
> to meet these goals.
>
> Thanks,
>
> Ray Walters
>
> Remote Solar
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches
mailing list