I just got back from being out of the office for a week+ and just read a
few ofthese. I hope this is not redundant.
6AWG is the size that meets several tests for exposed installations.By
that I mean that it is not protected. If you arerunning the array EGC
exposed, you would use at least 6AWG depending upon the size of the
overcurrent protection device towards the charge controller/array
disconnect. 250.120(C) and T250.122.
We have run into the conductor covering rating problemtoo. #4 can be
color coded so you can use black conductor. A reasonable inspector
should allow this for 6 since a lot of the non black coverings are not
holding up as well to sunlight as black. I think NEC2017 takes this
into consideration and allows you to color code because of the superior
performance of black coverings.
Chris
On 4/20/2018 9:00 AM, Dana wrote:
> That makes two of us that would like to understand, why #6? I think it dates to early grounding with grid tie systems.
> I remember back to 20+ years ago when the code required that the EGC was the size of the largest conductor which with 24 volt inverters was OOOO.
>
> ----------------------------------------------------------------------------
> Dana Orzel Great Solar Works, Inc.
> C - 208.721.7003 dana at solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136 www.solarwork.biz
> "Responsible Technologies for Responsible People since 1988"
> Please consider the environment before printing this email.
>
>
> -----Original Message-----
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Dave Angelini Offgrid Solar
> Sent: Thursday, April 19, 2018 3:57 PM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Looking for insulated #6 bare standoff
>
> Dana, I understand the need to use #6 in exposed places on the earth. I have had inspectors require the same wire size that is used to the battery. I have had them require the same size as the array wiring. I have never seen them do what they are doing to you so thanks for the info.... Be well! --Dave
>> The bare #8 is an EGC for #10 USE PV wire on the tracker to the array
>> mounted combiner box.
>>
>> ----------------------------------------------------------------------------
>> Dana Orzel Great Solar Works, Inc.
>> C - 208.721.7003 dana at solarwork.com
>> Idaho Contractor - # 028765 Idaho PV # 028374
>> NABCEP # 051112-136 www.solarwork.biz
>> "Responsible Technologies for Responsible People since 1988"
>> ï Please consider the environment before printing this email.
>>
>>
>> -----Original Message-----
>> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On
>> Behalf Of Hilton Dier
>> Sent: Thursday, April 19, 2018 3:39 PM
>> To: re-wrenches at lists.re-wrenches.org
>> Subject: [RE-wrenches] Looking for insulated #6 bare standoff
>>
>> Would #8 meet code? I thought that exposed ground wire had to be #6
>> minimum.
>>
>> Hilton Dier III
>> Renewable Energy Design
>> Missisquoi River Hydro LLC
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> .html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> .html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Christopher Warfel, PE
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
(401)466-8978
EEI logo <http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180420/d655b78b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180420/d655b78b/attachment.jpg>
More information about the RE-Wrenches
mailing list