[RE-wrenches] Conduit Across "Walkway"
Brian Mehalic
brian at solarenergy.org
Thu Apr 19 11:34:42 EDT 2018
Mark-
The 2018 IFC and IRC both state "Pathways shall be located in areas with
minimal obstructions, such as vent pipes, conduit or mechanical
equipment."
It must be permanently marked "WARNING PHOTOVOLTAIC POWER SOURCE" in
accordance with 690.31(G)(3) as well.
Brian Mehalic
NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
520.204.6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com
On Thu, Apr 19, 2018 at 11:02 AM, Mark Frye <markf at berkeleysolar.com> wrote:
> Folks,
>
> I have a 3 foot "walkway" on a roof pitch and between two separate arrays,
> as required.
>
> Is there anything that prevents me from running a conduit between the two
> arrays, across the "walkway"?
>
> Thanks,
>
> Mark Frye
>