[RE-wrenches] Location of DC disconnect vis-a-vis rapid shutdown exemption

Brian Mehalic brian at solarenergy.org
Mon Apr 16 09:44:57 EDT 2018


Hey y'all, I'm going to disagree about the NEC getting "worse and worse
when it comes to PV," (see disconnect and grounding requirements, for
instance!), but as with previous posters, that's just an opinion.

Regarding location - the 2014 version had very little to say about the
location of any rapid shutdown initiation device; 2017 adds the requirement
[690.12(C)] that RS initiation devices for one- and two-family dwellings be
readily accessible (defined in Article 100), AND outside the building.
Seems reasonable for a device that is intended to control energized
conductors to make it more safe to enter a building.

Cheers,


Brian Mehalic
NABCEP Certified Solar PV Installation Professionalâ„¢ R031508-59
520.204.6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com


On Mon, Apr 16, 2018 at 12:04 AM, Mark Frye <markf at berkeleysolar.com> wrote:

> Thanks Darryl.
>
> I guess I can add that I am in CA and so looked only at the 2014. I also
> looked at the 2017 article. Man, I have to say, my impression remains that
> really starting with 2008 the code has just gotten worse and worse when it
> comes to PV, but that is just me.
>
> Not really sure what might need to be "Outside readily accessible". Is
> there something other than 690.12 that I need to look at?
>
> Mark
> On 4/15/2018 8:26 PM, Darryl Thayer wrote:
>
> I think the code says Outside readily accessible,
>
> On Sun, Apr 15, 2018 at 12:22 PM, Mark Frye <markf at berkeleysolar.com>
> wrote:
>
>> Folks,
>>
>> As I recall, an inverter and it's integrated DC disconnect need only be
>> placed in an accessible location. I am thinking of putting an inverter high
>> up on the wall inside a garage. That would be OK vis-a-vis the location of
>> the disconnect (still accessible for maintenance).
>>
>> If I do put the inverter high up on the wall, I can limit my DC
>> conductors to less that 10 feet total from the array and less that 5 feet
>> inside the garage.
>>
>> That means I get the exemption from the rapid disconnect requirement,
>> right?
>>
>> There is nothing in the Code linking the accessibility of the DC
>> disconnect to the exemption from rapid shutdown, right?
>>
>> Mark Frye
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenches at lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180416/dfc52198/attachment.htm>


More information about the RE-Wrenches mailing list