[RE-wrenches] Clearance clarification please

Brian Mehalic brian at solarenergy.org
Wed Apr 4 11:28:09 EDT 2018


Yes!  And the IFC and IRC both allow local fire officials to basically
require, or allow, whatever they want (Exception 2 to IFC 1204.2 and IRC
R324.6).


Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
520.204.6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com


On Wed, Apr 4, 2018 at 9:22 AM, Darryl Thayer <darylsolar1 at gmail.com> wrote:

> Thank you good comments, facts, i am in Mn my last 3 installs the fire
> marshal said he did not care, he would use the north side of the roof or
> not at all.
>
> On Wed, Apr 4, 2018, 9:53 AM William Miller <william at millersolar.com>
> wrote:
>
>> Darryl:
>>
>>
>>
>> If you are talking about California, I must respectfully disagree.  If
>> you are not talking about California, I am ignorant.
>>
>>
>>
>> California Fire Code, 2016 version, states the following for group R-3
>> buildings (which I am fairly certain includes single family homes).  This
>> includes provisions for pitched roofs.  Upon first reading, I do not see
>> any improvements over the previous version (2012) except that it appears
>> clearance from valleys has reduced from 36” to 18”.
>>
>>
>>
>> These regulations are implemented by local fire Marshalls in California
>> (sometimes the same person as the Chief, sometimes not).  This gives the
>> Marshalls complete discretion.  I have had good luck negotiating with
>> Marshalls and finding good compromises.
>>
>>
>>
>> Excerpt from 2016 California fire code.
>>
>>
>>
>> *605.11.1.1 Roof access points. Roof access points*
>>
>> *shall be located in areas that do not require the placement*
>>
>> *of ground ladders over openings such as windows*
>>
>> *or doors, and located at strong points of building construction*
>>
>> *in locations where the access point does not*
>>
>> *conflict with overhead obstructions such as tree limbs,*
>>
>> *wires or signs.*
>>
>>
>>
>> *605.11.1.2 Solar photovoltaic systems for Group R-3*
>>
>> *buildings. Solar photovoltaic systems for Group R-3*
>>
>> *buildings shall comply with Sections 605.11.1.2.1*
>>
>> *through 605.11.1.2.5.*
>>
>> *Exception: These requirements shall not apply to*
>>
>> *structures designed and constructed in accordance*
>>
>> *with the California Residential Code.*
>>
>> *605.11.1.2.1 Size of solar photovoltaic array. Each*
>>
>> *photovoltaic array shall be limited to 150 feet (45*
>>
>> *720 mm) by 150 feet (45 720 mm). Multiple arrays*
>>
>> *shall be separated by a 3-foot-wide (914 mm) clear*
>>
>> *access pathway.*
>>
>> *605.11.1.2.2 Hip roof layouts. Panels and modules*
>>
>> *installed on Group R-3 buildings with hip roof layouts*
>>
>> *shall be located in a manner that provides a 3-*
>>
>> *foot-wide (914 mm) clear access pathway from the*
>>
>> *eave to the ridge on each roof slope where panels*
>>
>> *and modules are located. The access pathway shall*
>>
>> *be at a location on the building capable of supporting*
>>
>> *the fire fighters accessing the roof.*
>>
>> *Exception: These requirements shall not apply to*
>>
>> *roofs with slopes of two units vertical in 12 units*
>>
>> *horizontal (2:12) or less.*
>>
>> *605.11.1.2.3 Single-ridge roofs. Panels and modules*
>>
>> *installed on Group R-3 buildings with a single*
>>
>> *ridge shall be located in a manner that provides two,*
>>
>> *3-foot-wide (914 mm) access pathways from the*
>>
>> *eave to the ridge on each roof slope where panels*
>>
>> *and modules are located.*
>>
>> *Exception: This requirement shall not apply to*
>>
>> *roofs with slopes of two units vertical in 12 units*
>>
>> *horizontal (2:12) or less.*
>>
>> *605.11.1.2.4 Roofs with hips and valleys. Panels*
>>
>> *and modules installed on Group R-3 buildings with*
>>
>> *roof hips and valleys shall not be located closer than*
>>
>> *18 inches (457 mm) to a hip or a valley where panels/*
>>
>> *modules are to be placed on both sides of a hip or*
>>
>> *valley. Where panels are to be located on only one*
>>
>> *side of a hip or valley that is of equal length, the*
>>
>> *panels shall be permitted to be placed directly adjacent*
>>
>> *to the hip or valley.*
>>
>> *Exception: These requirements shall not apply to*
>>
>> *roofs with slopes of two units vertical in 12 units*
>>
>> *horizontal (2:12) or less.*
>>
>> *605.11.1.2.5 Allowance for smoke ventilation*
>>
>> *operations. Panels and modules installed on Group*
>>
>> *R-3 buildings shall be located not less than 3 feet*
>>
>> *(914 mm) from the ridge** in order to allow for fire*
>>
>> *department smoke ventilation operations.*
>>
>> *Exception: Panels and modules shall be permitted*
>>
>> *to be located up to the roof ridge where an*
>>
>> *alternative ventilation method approved by the*
>>
>> *fire chief has been provided or where the fire*
>>
>> *chief has determined vertical ventilation techniques*
>>
>> *will not be employed.*
>>
>> *605.11.1.2.6 Locations of DC conductors. Conduit,*
>>
>> *wiring systems, and raceways for photovoltaic circuits*
>>
>> *shall be located as close as possible to the*
>>
>> *ridge or hip or valley and from the hip or valley as*
>>
>> *directly as possible to an outside wall to reduce trip*
>>
>> *hazards and maximize ventilation opportunities.*
>>
>> *Conduit runs between sub arrays and to DC combiner*
>>
>> *boxes shall be installed in a manner that minimizes*
>>
>> *the total amount of conduit on the roof by*
>>
>> *taking the shortest path from the array to the DC*
>>
>> *combiner box. The DC combiner boxes shall be*
>>
>> *located such that conduit runs are minimized in the*
>>
>> *pathways between arrays. DC wiring shall be*
>>
>> *installed in metallic conduit or raceways when*
>>
>> *located within enclosed spaces in a building. Conduit*
>>
>> *shall run along the bottom of load bearing*
>>
>> *members.*
>>
>>
>>
>>
>>
>> [image: Gradient Cap_mini]
>> Lic 773985
>> millersolar.com <http://www.millersolar.com/>
>> 805-438-5600
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
>> Behalf Of *Darryl Thayer
>> *Sent:* Tuesday, April 03, 2018 8:51 PM
>> *To:* newrewrenches
>> *Subject:* Re: [RE-wrenches] Clearance clarification please
>>
>>
>>
>> It is in the building code.  It is for commercial flat roofs not for
>> residential
>>
>>
>>
>> On Tue, Apr 3, 2018, 2:52 PM <chris at oasismontana.com> wrote:
>>
>> Hey folks:
>>
>>
>>
>> What section of the Code relates to the 3' clearance for a solar array?
>> …as in, the roof area around the array.   I’ve been scrutinizing the NEC
>> til my eyes are crossed…..
>>
>>
>>
>> THANKS!
>>
>>
>>
>>
>>
>> Chris Daum
>>
>> Oasis Montana Inc.
>>
>> 406-777-4309
>>
>> 406-777-4309 fax
>>
>> www.oasismontana.com
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180404/4f747b0e/attachment.htm>


More information about the RE-Wrenches mailing list