Section 1204.4 of the 2018 IFC exempts free-standing, ground-mounted arrays
from setback requirements, but does require a clear, brush-free area of 10
feet for ground-mounted arrays.
Of course this all depends on what codes your jurisdiction enforces - no
California, the rest of the country doesn't always do it exactly the way
you do :)
Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
520.204.6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com
On Wed, Apr 4, 2018 at 9:15 AM, Dave Angelini Offgrid Solar <
offgridsolar at sti.net> wrote:
> It always depends on who you are working with ! Because of you folks
> putting solar panels on roofs, I have had a few fire Captains ask about
> clearances on ground mounted trackers:(
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> > Darryl:
> >
> >
> >
> > If you are talking about California, I must respectfully disagree. If
> you
> > are not talking about California, I am ignorant.
> >
> >
> >
> > California Fire Code, 2016 version, states the following for group R-3
> > buildings (which I am fairly certain includes single family homes). This
> > includes provisions for pitched roofs. Upon first reading, I do not see
> > any improvements over the previous version (2012) except that it appears
> > clearance from valleys has reduced from 36†to 18†.
> >
> >
> >
> > These regulations are implemented by local fire Marshalls in California
> > (sometimes the same person as the Chief, sometimes not). This gives the
> > Marshalls complete discretion. I have had good luck negotiating with
> > Marshalls and finding good compromises.
> >
> >
> >
> > Excerpt from 2016 California fire code.
> >
> >
> >
> > *605.11.1.1 Roof access points. Roof access points*
> >
> > *shall be located in areas that do not require the placement*
> >
> > *of ground ladders over openings such as windows*
> >
> > *or doors, and located at strong points of building construction*
> >
> > *in locations where the access point does not*
> >
> > *conflict with overhead obstructions such as tree limbs,*
> >
> > *wires or signs.*
> >
> >
> >
> > *605.11.1.2 Solar photovoltaic systems for Group R-3*
> >
> > *buildings. Solar photovoltaic systems for Group R-3*
> >
> > *buildings shall comply with Sections 605.11.1.2.1*
> >
> > *through 605.11.1.2.5.*
> >
> > *Exception: These requirements shall not apply to*
> >
> > *structures designed and constructed in accordance*
> >
> > *with the California Residential Code.*
> >
> > *605.11.1.2.1 Size of solar photovoltaic array. Each*
> >
> > *photovoltaic array shall be limited to 150 feet (45*
> >
> > *720 mm) by 150 feet (45 720 mm). Multiple arrays*
> >
> > *shall be separated by a 3-foot-wide (914 mm) clear*
> >
> > *access pathway.*
> >
> > *605.11.1.2.2 Hip roof layouts. Panels and modules*
> >
> > *installed on Group R-3 buildings with hip roof layouts*
> >
> > *shall be located in a manner that provides a 3-*
> >
> > *foot-wide (914 mm) clear access pathway from the*
> >
> > *eave to the ridge on each roof slope where panels*
> >
> > *and modules are located. The access pathway shall*
> >
> > *be at a location on the building capable of supporting*
> >
> > *the fire fighters accessing the roof.*
> >
> > *Exception: These requirements shall not apply to*
> >
> > *roofs with slopes of two units vertical in 12 units*
> >
> > *horizontal (2:12) or less.*
> >
> > *605.11.1.2.3 Single-ridge roofs. Panels and modules*
> >
> > *installed on Group R-3 buildings with a single*
> >
> > *ridge shall be located in a manner that provides two,*
> >
> > *3-foot-wide (914 mm) access pathways from the*
> >
> > *eave to the ridge on each roof slope where panels*
> >
> > *and modules are located.*
> >
> > *Exception: This requirement shall not apply to*
> >
> > *roofs with slopes of two units vertical in 12 units*
> >
> > *horizontal (2:12) or less.*
> >
> > *605.11.1.2.4 Roofs with hips and valleys. Panels*
> >
> > *and modules installed on Group R-3 buildings with*
> >
> > *roof hips and valleys shall not be located closer than*
> >
> > *18 inches (457 mm) to a hip or a valley where panels/*
> >
> > *modules are to be placed on both sides of a hip or*
> >
> > *valley. Where panels are to be located on only one*
> >
> > *side of a hip or valley that is of equal length, the*
> >
> > *panels shall be permitted to be placed directly adjacent*
> >
> > *to the hip or valley.*
> >
> > *Exception: These requirements shall not apply to*
> >
> > *roofs with slopes of two units vertical in 12 units*
> >
> > *horizontal (2:12) or less.*
> >
> > *605.11.1.2.5 Allowance for smoke ventilation*
> >
> > *operations. Panels and modules installed on Group*
> >
> > *R-3 buildings shall be located not less than 3 feet*
> >
> > *(914 mm) from the ridge** in order to allow for fire*
> >
> > *department smoke ventilation operations.*
> >
> > *Exception: Panels and modules shall be permitted*
> >
> > *to be located up to the roof ridge where an*
> >
> > *alternative ventilation method approved by the*
> >
> > *fire chief has been provided or where the fire*
> >
> > *chief has determined vertical ventilation techniques*
> >
> > *will not be employed.*
> >
> > *605.11.1.2.6 Locations of DC conductors. Conduit,*
> >
> > *wiring systems, and raceways for photovoltaic circuits*
> >
> > *shall be located as close as possible to the*
> >
> > *ridge or hip or valley and from the hip or valley as*
> >
> > *directly as possible to an outside wall to reduce trip*
> >
> > *hazards and maximize ventilation opportunities.*
> >
> > *Conduit runs between sub arrays and to DC combiner*
> >
> > *boxes shall be installed in a manner that minimizes*
> >
> > *the total amount of conduit on the roof by*
> >
> > *taking the shortest path from the array to the DC*
> >
> > *combiner box. The DC combiner boxes shall be*
> >
> > *located such that conduit runs are minimized in the*
> >
> > *pathways between arrays. DC wiring shall be*
> >
> > *installed in metallic conduit or raceways when*
> >
> > *located within enclosed spaces in a building. Conduit*
> >
> > *shall run along the bottom of load bearing*
> >
> > *members.*
> >
> >
> >
> >
> >
> > [image: Gradient Cap_mini]
> > Lic 773985
> > millersolar.com <http://www.millersolar.com/>
> > 805-438-5600
> >
> >
> >
> > *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On
> > Behalf Of *Darryl Thayer
> > *Sent:* Tuesday, April 03, 2018 8:51 PM
> > *To:* newrewrenches
> > *Subject:* Re: [RE-wrenches] Clearance clarification please
> >
> >
> >
> > It is in the building code. It is for commercial flat roofs not for
> > residential
> >
> >
> >
> > On Tue, Apr 3, 2018, 2:52 PM <chris at oasismontana.com> wrote:
> >
> > Hey folks:
> >
> >
> >
> > What section of the Code relates to the 3' clearance for a solar array?
> > …as in, the roof area around the array. I’ve been scrutinizing the
> > NEC til
> > my eyes are crossed…..
> >
> >
> >
> > THANKS!
> >
> >
> >
> >
> >
> > Chris Daum
> >
> > Oasis Montana Inc.
> >
> > 406-777-4309
> >
> > 406-777-4309 fax
> >
> > www.oasismontana.com
> >
> >
> >
> >
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> >
>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180404/34f328ac/attachment.htm>
More information about the RE-Wrenches
mailing list