[RE-wrenches] Outback OpticsRE and FlexNet DC shunts monitoring question
Dan Fink
danbob88 at gmail.com
Fri Mar 16 22:43:43 EDT 2018
Esteemed Wrenches;
We recently installed OpticsRE monitoring for an existing off-grid site in
Southern Colorado. It is 24v battery bank, 2.2kW PV, 2 Outback Flexmax 60
controllers, nice old Trace SW inverter, and new wind turbine + controller
to replace a failed Whisper 200 with worn out furl and yaw bushings.
We installed a FlexMaxDC shunt monitor into the Outback Hub, with the old
TriMetric shunt set as "inverter" and a new wind turbine shunt set as "wind"
We removed the existing Bogart TriMetric and replaced it with the Mate 3s
and , everything is working fine for remote monitoring. But because the
Mate can't talk to the Trace inverter, it appears the PV input is
subtracting from the inverter output on that shunt. Thinking that moving
the PV input to the other side of the shunt will fix that, as the charge
controllers are talking to OpticsRE just fine.
Questions:
When the gasoline generator starts from low SOC (from the Trace SW relay)
will the FlexMaxDC Shunt A show a positive charging gain from the generator
or does FlexmaxDC only show one way (load or charge)? I don't see any way
of separating inverter load vs. generator gain. We will test this next
month down there, but it's 5 hours away, we just want to be prepared.
Is there any way to graph the FlexMaxDC shunts on the main online
dashboard? They seem like a neglected child, only accessible by clicking
multiple menus, and just downloading data to a spreadsheet. The idea was to
show the client on a real-time graph how much the wind turbine is
contributing versus PV.
For that main dashboard, we realize that without an Outback
inverter/charger, the graph will never show gasoline "generator" but if it
showed inverter loads as a gain, that would be enough.
Still getting our heads wrapped around OpticsRE, but the setup and
commissioning was very easy, and it does work, after running a bunch of
CAT5 hardwired; Concrete/Adobe structure filled with remesh blocked all
efforts for wifi, The wifi router is located in the solar thermal room
downstairs (the ReSol monitoring works great on the thermal) and barely a
whiff of it upstairs at the electrical control room....OpticsRE seems to
need a pretty robust internet connection.
Any thoughts appreciated, this is our first OpticsRE install.
Dan Fink
Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180316/1c3d3665/attachment.htm>
More information about the RE-Wrenches
mailing list