[RE-wrenches] heating a lithium battery bank
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Tue Feb 27 13:13:34 EST 2018
The LG RESU series will trip it's breaker at around 10% Soc. It will
require a human unless the LVD on the inverter is set higher than the
battery. Yes Sir it is our responsibility to educate our users or have
plane tickets (:
Will be installing the Discover battery soon into Xanbus.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
> Hi Drake,
>
> I agree. Li-ion batteries, like lead batteries, should always have a human
> overseer. This is a difficult reality to convey in our set-it-forget it,
> automated world.
>
> One function of a Li-ion battery EMS or BMS is to prevent over discharge.
> Once any battery cell reaches the lower limit, the battery will turn off.
> For many systems, once charge current is again detected, the battery will
> turn on. Some will not and require a user to turn the battery back on. You
> can also install an external LVD device to stop power use at a higher SoC.
>
> As wrenches, its our responsibility to know our product and educate the
> customer. Too often, this does not happen.
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
>
>
>
> On Feb 27, 2018, at 7:11 AM, drake.chamberlin at redwoodalliance.org wrote:
>
> Snow on the array could be a very big problem with the heater load,
> inverter idle current and anything else that might be left on. Extended
> periods of heavy clouds can reduce power generation to be less than
> system's internal losses. It seems like a pretty big gamble to leave an
> expensive battery bank unattended, that can not go below freezing, and is
> dependent on array power to prevent freezing.
>
> If AGMs survive in this application, it might be better to stay with this
> technology.
>
>
> ----- Original Message -----
> From: offgridsolar at sti.net "RE-wrenches"
> <re-wrenches at lists.re-wrenches.org>
> To:"RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Cc:
> Sent:Mon, 26 Feb 2018 10:36:29 -0800 (PST)
> Subject:Re: [RE-wrenches] heating a lithium battery bank
>
>
> Hello Daniel,
>
> I will give this some thought. What lithium make? The ones I have looked
> at log the temperature for warranty so that might negate the value a bit.
> The high temp is just as bad in your case here.
>
> Since this has been working well I am assuming snow on the panels is not
> an issue?
>
> Building a battery box that was cooled (small fan) from conditioned space
> is what I have done. The wall between the garage and living space is
> perfect. This won't help when the house is cold (unattended) much. It
> won't help if the house is allowed to get hot either.
>
> Some of the Lion batteries are actually listed for living space. The LG
> is. I don't do that with mine though. Hmmm
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
>> Hello Wrenches, here is a fun one for you all.
>>
>>
>>
>> The client you all helped me with earlier this year is now considering
>> changing out their AGM off grid bank with a lithium battery bank before
>> the
>> next winter. I looked into this, as we have been eying the various
>> lithium
>> options for 2+yrs now, but not bit the bullet and really designed a bank
>> into a system.
>>
>>
>>
>> The main issue I am trying to consider is this. The cabin is not
>> occupied
>> during most of the winter, and the batteries are in the unconditioned,
>> but
>> attached, garage. They drain the plumbing system and shut off all
>> breakers
>> except the ones that power the internet, chest freezer, and security
>> system.
>> As such, the battery bank has routinely gotten below freezing, sometimes
>> staying there for 1-2 weeks. This is not an issue with AGM's, within
>> reason.
>> The battery bank has never gotten below 20F over the last 2 winters,
>> where
>> the site has seen below zero temps for brief periods. But the AGMs
>> likely
>> produce more heat during a charge than lithium's, and they have
>> significantly more thermal mass to ride through the really cold nights.
>>
>>
>>
>> Lithium batteries, to the best of my knowledge, can be below freezing
>> during
>> storage. But to safely charge, they must be above 32F. So the thought
>> was
>> to
>> provide an insulated battery box, and design in some small heating
>> system
>> that is set to 40-45F. The first thought was a low power fiberglass
>> heating
>> pad like is sometimes used for livestock to give them a slightly warmed
>> place to lay down. Then tie that to a thermostat with a sensor on the
>> battery bank. I would of course need to try to account for the extra
>> load
>> in
>> the battery bank sizing. They array is more than is needed right now so
>> I
>> do
>> not worry about it's ability to compensate when the sun is shining.
>>
>>
>>
>> In theory this could be ok, but I worry about the summer. Will the
>> insulated
>> enclosure cause the opposite issue during the summer, the batteries
>> getting
>> too hot? I have seen the AGM bank go to 110F at one point in Aug 2016.
>> But
>> with the lower internal resistance of the lithium's, maybe this is less
>> likely to be an issue. Do any of you wrenches have any experience with
>> this
>> unconditioned setup?
>>
>>
>>
>> With Regards,
>>
>>
>>
>> Daniel Young,
>>
>> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> http://members.sti.net/offgridsolar/
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridsolar at sti.net
text 209 813 0060
More information about the RE-Wrenches
mailing list