Hello Lones here.
 When an ac source is accepted by the inverter. The rely connects the ac input directly to the ac output. The relay is (should be) protected by a 50 amp breaker
If there is an ac load of 8KW or 33 ac amps the remaining current is available to be used by the inverter for battery charging. If the load increases above 8k charging is reduced to honor the loads first. If the loads chew up all 50 amps charging will be reduced to zero. Above 50 and the breaker should trip or damage to the relay may result.
 It is possible to use Support Mode. This sets a limit on the amount of current passing through from the source to the loads. Any amount above the set point will be supplied from the batteries. If the ac input current is set to 25 ac amps. Any load above the 25 amps will come from the batteries. Sustained loads above this adjustable set point could possibly deplete the batteries. If the load drops below the 25amp charging will resume.
It is possible have an ac source and deplete the batteries.
Loads first Charging 2nd.
I hope this helps.
Take Care All

-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Angelini Offgrid Solar
Sent: Saturday, February 24, 2018 9:16 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Radian throughput power

You are missing the charging of the battery! That is where (your numbers) the 12KW - 8KW can go!


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060

> Wrenches,
>
>              I spoke with tech support at Outback recently 
> and was told the max output of the Radian at the output terminals is 
> 8KW, even if there is an external AC source connected to one of the AC 
> IN terminals of the Radian.
>
>              However, on page 18 of the GS8048 manual:  
> "When it (transfer relay) closes the L1 input and output terminals 
> become electrically common."  ...same for L2 input and output. then, 
> "the relay contacts are limited to 55 amps per phase or leg".  Since 
> there is no 55 amp circuit breaker to protect that relay a 50 amp 2 
> pole breaker would be used.  This means you would have 50A X 240 Vac 
> (12KW) at the output terminals, correct?
>
>              Am I missing something?  Thanks,
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
> .html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



More information about the RE-Wrenches mailing list