Wrenches,

             I spoke with tech support at Outback recently and was told 
the max output of the Radian at the output terminals is 8KW, even if 
there is an external AC source connected to one of the AC IN terminals 
of the Radian.

             However, on page 18 of the GS8048 manual:  "When it 
(transfer relay) closes the L1 input and output terminals become 
electrically common."  ...same for L2 input and output. then, "the relay 
contacts are limited to 55 amps per phase or leg".  Since there is no 55 
amp circuit breaker to protect that relay a 50 amp 2 pole breaker would 
be used.  This means you would have 50A X 240 Vac (12KW) at the output 
terminals, correct?

             Am I missing something?  Thanks,

Bill