[RE-wrenches] Older iCel System Lithium Ion Batteries

Gary Rochlin g.rochlin at gmail.com
Fri Feb 16 18:00:12 EST 2018


Thank you for the input.  I’m going to purchase a 48V Charger and charger each module and monitor it closely.   

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Saturday, February 10, 2018 4:03 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Older iCel System Lithium Ion Batteries

 

Is there not a concern that if the batteries are showing such low voltage that they will not accept current, and the voltage will rise to module voltage and put array voltage on the output of the charge controller?

 

On Sat, Feb 10, 2018 at 12:24 PM, Ray <ray at solarray.com <mailto:ray at solarray.com> > wrote:

Allan has a good approach as long as you are there to monitor it.  The wiring is already there, you just have jump the array positive to the controller output.  ( a little double lugging never hurt anyone....?!!.)  

Even higher voltage arrays with MPPT can be used this way.  They will just put out close to their short circuit current, as the batteries will pull the array voltage way down on the IV curve. 

Ray Walters

Remote Solar

 

On 2/10/18 1:37 AM, Sindelar Solar wrote:

Gary, you might try an old-fashioned approach: bypass the controller to send the array straight to the batteries until threshold voltage is reached. More specifically, bypass one of the controllers; assuming 48, 60 or 72 Vnom depending on array. Let the other controller remain in normal operation. Send the unregulated array to bring initial battery voltage up; then the other controller takes over and the one that was bypassed now is reconnected. Better if the unregulated array is the smaller of the two, I would suspect.

What I'm suggesting will work with flooded lead-acid, and likely VRLA lead-acid as well, as long as the unregulated array is taken out of the system before voltage exceeds bulk. It may not work at all with these Li-I, as I have no experience with restoring them. Daryl may well be right about being unrestorable below a threshold voltage; also the batteries may need an operational BMS to take a charge. So this is perhaps just food for thought.

Allan

-- 

Allan Sindelar
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com> 
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 <tel:(505)%20780-2738>  cell

On 2/9/2018 6:16 PM, Gary Rochlin wrote:

Does anyone have any information or specifications for an older circa 2010-2012 iCel System Lithium Ion Battery.  We are doing a repair on an older 48V Lithium Ion system consisting of 3-6 ICel batteries wired in parallel and 1 Xantrex 6848 and 2 Xantrex Conext MPPT 60 150 Solar Charge controllers.  Via a surge from SCE system shut down and sat before we were called in.  Batteries are sitting at 6.67V and the charge controller will not turn on unless the batteries are at 40V since at the time they were made for lead acid batteries.  I’m looking at finding the way to charge the iCel  batteries or goose the charge controller into thinking 40V are coming from the batteries.  I think I’m making sense here.  

Blue Sky Energy 

 <mailto:mtnrider at verizon.net> g.rochlin at blue-sky-energy.com <http://blue-sky-energy.com> 

_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

 

 

_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 
 

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 



 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180216/43e760a2/attachment.htm>


More information about the RE-Wrenches mailing list