The solar self consumption mode is a requirement in order to qualify for
the SGIP incentive for PV-paired systems. For residential systems, the
storage system must discharge a minimum of 52 full cycles per year which
equates to once per week on average.
In addition, solar self consumption mode can save a little money by a)
reducing the non-bypassable charges associated with NEM2
<https://www.pge.com/en_US/residential/solar-and-vehicles/green-energy-incentives/solar-and-renewable-metering-and-billing/net-energy-metering-program-tracking/net-energy-metering-and-tracking-faq.page>
and b) potentially reduce some Time Of Use (TOU) peak rate energy
consumption. It's a particularly good choice for folks who have electric
vehicles on the EV
<https://www.pge.com/tariffs/assets/pdf/tariffbook/ELEC_SCHEDS_EV.pdf> rate
where the peak rates go to 9:00 pm and part peak goes to 11:00 pm.
Generally speaking, we're seeing TOU peak periods shift later and later in
California.
August
On Tue, Feb 13, 2018 at 11:34 AM, Marco Mangelsdorf <marco at pvthawaii.com>
wrote:
> Is there a financial benefit to the customer-generator to choose the
> self-powered mode, August?
>
> marco
>
> On Tuesday, February 13, 2018, August Goers <august at luminalt.com> wrote:
>
>> Yes, PG&E. The Self Generation Incentive Program (SGIP) created a flood
>> of applications and PG&E is having a hard time keeping up. Hopefully it
>> will get easier.
>>
>> We are enabling self-consumption and backup modes. The Powerwall charges
>> daily from the solar and then discharges to a owner-set minimum reserve
>> capacity.
>>
>> August
>>
>> *August*
>>
>> Luminalt Energy Corporation
>>
>> o: 415.641.4000 <(415)%20641-4000>
>>
>> www.luminalt.com
>>
>>
>>
>> On Tue, Feb 13, 2018 at 8:30 AM, Marco Mangelsdorf <marco at pvthawaii.com>
>> wrote:
>>
>>> Hey August.
>>>
>>> By utility I assume that you are talking about PG&E.
>>>
>>> What's the hang up? And are running the PWs in back-up power only mode
>>> or daily cycling mode?
>>>
>>> In either case, the addition of PW does not add to the generating
>>> capacity of the solar facility.
>>>
>>> marco
>>>
>>> On Tuesday, February 13, 2018, August Goers <august at luminalt.com> wrote:
>>>
>>>> Marco,
>>>>
>>>> Thanks for sharing, it is good to hear details from an installer who is
>>>> living with a Powerwall. We starting selling the Powerwall 2 in 2017 and
>>>> have worked up a large pipeline. We have about 20 installed so far, but are
>>>> still waiting on utility permission to operate which is taking a long time.
>>>> We have spent a good deal of time commissioning and testing each system.
>>>> For the most part, our experience has been good although the commissioning
>>>> software and internet connectivity features have been buggy. Hopefully
>>>> those are issues that will be ironed out by Tesla. Otherwise, we've had the
>>>> systems correctly operate in on-grid and off-grid modes with both Solaredge
>>>> and SunPower Equinox AC coupled systems.
>>>>
>>>> We installed conventional lead acid battery backup systems for over 10
>>>> years and I can confidently say that Tesla's Powerwall and Gateway setup
>>>> is truly market-disruptive. The design flexibility of the Gateway setup,
>>>> the small size, minimal labor to install, and performance blow other
>>>> systems out of the water. I hope that other manufacturers are able to catch
>>>> up with this type of design.
>>>>
>>>> Best,
>>>>
>>>> August
>>>>
>>>> *August Goers*
>>>>
>>>> Luminalt Energy Corporation
>>>>
>>>> o: 415.641.4000 <(415)%20641-4000>
>>>>
>>>> www.luminalt.com
>>>>
>>>>
>>>>
>>>> On Sat, Feb 10, 2018 at 12:23 PM, Marco Mangelsdorf <
>>>> marco at pvthawaii.com> wrote:
>>>>
>>>>>
>>>>>
>>>>> *Aloha Wrenches,*
>>>>>
>>>>>
>>>>> *I thought I'd share my own experiences with the Powerwall as my
>>>>> company is now launching a program to add PW to existing NEM systems since
>>>>> the vast majority of them do not have storage which means that if the grid
>>>>> goes down, so does their PV system. (With the exception of the SMA SB line
>>>>> and their Secure Power Supply.)*
>>>>>
>>>>>
>>>>> *And no, I'm not a shill or toadie for Tesla.*
>>>>>
>>>>>
>>>>> *marco *
>>>>>
>>>>> *I wanted to walk my own talk. Before we launched adding Powerwall to
>>>>> existing Net Energy Metered solar electric systems, I wanted to make sure
>>>>> that what was promised on paper would work in the real world. I added
>>>>> Powerwall to my NEM system last year and have been monitoring and testing
>>>>> it during normal grid-on and grid outage modes. And I’m very pleased to
>>>>> report that Powerwall has performed flawlessly and as expected.*
>>>>>
>>>>>
>>>>>
>>>>> *When used in a NEM system, Powerwall is programmed to be in “Backup”
>>>>> mode. When utility power is on, Powerwall stands ready in a full state of
>>>>> charge for any power outage. During normal grid-on conditions, my Powerall
>>>>> takes about .6 kilowatt-hours every other day to stay fully charged. Over
>>>>> the course of the month, this Powerwall’s electricity consumption comes to
>>>>> about 9 kWhs or about $3/month at the current HELCO R rate.*
>>>>>
>>>>>
>>>>>
>>>>> *I have turned the utility power off to my home on a number of
>>>>> occasions in order to experience how Powerwall would perform in a simulated
>>>>> grid outage. When the grid goes down, my house effectively becomes a
>>>>> self-generating micro-grid. That is, my photovoltaic system (solar modules
>>>>> and inverters) and Powerwall (battery storage and integrated inverter) form
>>>>> a power grid with energy being created and stored and then consumed by my
>>>>> electric loads.*
>>>>>
>>>>>
>>>>>
>>>>> *Several things I noted from my simulated grid outages:*
>>>>>
>>>>> *· I purposefully overloaded Powerwall by turning on my
>>>>> electric dryer and electric oven at the same time. As expected, since the
>>>>> maximum output of Powerwall is 5 kilowatts, it shutdown. Meaning that all
>>>>> the power in my house went off. Within seconds, Powerwall reset itself and
>>>>> the power came back on, with the dryer and oven having shut down after the
>>>>> power went off. If power does not come back on after your Powerwall trips
>>>>> off, you will need to turn off those high-power loads and reset Powerwall
>>>>> by turning its black on-off switch, located on the right side of the unit,
>>>>> from on to off and then on again. The important takeaway: during a utility
>>>>> outage, you will need to be careful as far as operating heavy electric
>>>>> loads, especially 240 volt appliances both from the perspective of
>>>>> overloading your Powerwall and rapidly drawing down the battery capacity,
>>>>> especially at night.*
>>>>>
>>>>> *· The magic of frequency shifting. Without getting into too
>>>>> much techno-talk, this is the story of frequency shifting. Normal utility
>>>>> frequency is 60 hertz (Hz). PV inverters require the utility frequency to
>>>>> be at or near 60 Hz in order to operate. During a grid outage, Powerwall
>>>>> effectively establishes grid quality power (120/240 volts at 60 Hz),
>>>>> allowing a micro grid to operate with solar providing power to your house
>>>>> loads (during daylight hours) and charge Powerwall as needed. During the
>>>>> day with the loads being met by your PV system and Powerwall being at or
>>>>> near full state of charge (97-100 percent), Powerwall will shift the
>>>>> frequency from 60 to 66 Hz in order to turn off the PV inverter(s). That
>>>>> is, the PV inverter(s) see the frequency out of spec and shut down as
>>>>> they’re expected and required to do. Why? Because with Powerwall at or
>>>>> near full and the house loads being met, there’s nowhere for any additional
>>>>> solar generation to go. Powerwall will wait for its the state of charge to
>>>>> drop below 96-97 percent before shifting the frequency back to 60 Hz which
>>>>> allows the PV system to restart and generate solar power again. This
>>>>> frequency shifting can take place repeatedly over the course of the day
>>>>> depending on load demands, solar potential and Powerwall state of charge
>>>>> and is perfectly normal and does not damage the PV inverters.*
>>>>>
>>>>> *· **66 Hz and home appliances: when Powerwall is at 66 Hz,
>>>>> some of your house loads may be affected. What I and other Powerwall
>>>>> owners have noticed, while not a comprehensive list, can include:
>>>>> electronic clocks running fast, motors sounding different (microwave,
>>>>> washing machine, pumps), uninterruptible power sources (UPS) not charging
>>>>> and going into back-up power mode, appliances having a computer behaving
>>>>> unusually.*
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive: http://www.mail-archive.com/re
>>>>> -wrenches at lists.re-wrenches.org/maillist.html
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>>>
>>>>>
>>>>>
>>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenches at lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20180213/58172cd1/attachment.htm>
More information about the RE-Wrenches
mailing list